    I am enjoying my first woodstove - Jotul Rangeley recently installed. It sits on a Type 1 ember protection hearth pad, which meets Jotul requirements. Im concerned that the pad is hot under the stove and wonder if something's amiss with the bottom heat shield. A friend told me it's cool under her Vermont Castings stove, so Im now more worried. Thoughts/advice would be appreciated. Thanks.
     

    Helpful Sponsor Ads!





  2. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,196
    Likes Received:
    7,340
    Loc:
    South Puget Sound, WA
    Welcome to the forum. Each stove is different. Can you put your hand on the hearth below the stove briefly? If yes, for how long?
     
    Collapse Signature Expand Signature
  3. cc rangeley

    cc rangeley
    Expand Collapse
    New Member

    Joined:
    Jan 7, 2013
    Messages:
    37
    Likes Received:
    0
    The front is cool, but I stuck my stovetop thermometer on the pad beneath the hot area and it looks like it's about 150 degrees.
     
  4. cc rangeley

    cc rangeley
    Expand Collapse
    New Member

    Joined:
    Jan 7, 2013
    Messages:
    37
    Likes Received:
    0
    Should've added I can only put my hand there for a few seconds.
     
  5. ArsenalDon

    ArsenalDon
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 16, 2012
    Messages:
    751
    Likes Received:
    191
    Loc:
    Meadow Valley, CA
    My IR shows my hearth pad about 150-160 at the hottest
     
    Collapse Signature Expand Signature
  6. cc rangeley

    cc rangeley
    Expand Collapse
    New Member

    Joined:
    Jan 7, 2013
    Messages:
    37
    Likes Received:
    0
    Is it an ember protection pad - or thermal? What's also a concern is that the pre-existing stone hearth that abuts the ember pad is also 150 degrees.
     
  7. ArsenalDon

    ArsenalDon
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 16, 2012
    Messages:
    751
    Likes Received:
    191
    Loc:
    Meadow Valley, CA
    Dunno. Stove installer sold it to us.
     
    Collapse Signature Expand Signature
  8. BobUrban

    BobUrban
    Expand Collapse
    Minister of Fire

    Joined:
    Jul 24, 2010
    Messages:
    1,902
    Likes Received:
    1,110
    Loc:
    Central Michigan
    The hottest part of my hearth is the floor right in front of the door. Those tiles get really warm when I have her cuising at 650-700 which is pretty common lately. I can stand on it with my bare feet and actually enjoy it but not doubt this is the "hot spot" I do not have any idea of the actual temp but I will pute my cheap rutland therm down there to get some idea. Because I can hold my hand to it and stand on it I do not believe it is a cause for concern but I am going to keep an eye on it and feel it from the bottom(basement) for peace of mind.

    ***Update*** using the same therm that I set on my stove - stove is cruising at 700 tile floor out front is just above 100 to 130 depending on where it is setting on the floor. Warm but not scary hot.
     
    Collapse Signature Expand Signature
  9. burnt03

    burnt03
    Expand Collapse
    Burning Hunk

    Joined:
    Oct 30, 2011
    Messages:
    239
    Likes Received:
    67
    Loc:
    Peachland, BC, Canada
    I remember a post on here a while back talking about something similar but I can't find it. It basically said that if you can touch it without burning yourself, you're good to go.

    Did a search for auto-ignition temperature of wood (assuming that's the first flammable thing the heat comes into contact with on your floor) and it comes back as 572 F. (http://www.engineeringtoolbox.com/fuels-ignition-temperatures-d_171.html)

    So, assuming I'm looking at the right factor, should be good :)
     
    Collapse Signature Expand Signature
  10. Jags

    Jags
    Expand Collapse
    Moderate Moderator
    Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    16,969
    Likes Received:
    5,765
    Loc:
    Northern IL
    The Isle Royale only requires ember protection, so I doubt that there is much thermal capacity of his hearth pad. It is acceptable to have about an 80F rise of wall temp over ambient room temp, so I would think the same would hold true for floor temp. Sounds like you are right at the outer edge of those temps.
     
    Collapse Signature Expand Signature
  11. cc rangeley

    cc rangeley
    Expand Collapse
    New Member

    Joined:
    Jan 7, 2013
    Messages:
    37
    Likes Received:
    0
    The top of the ember pad is 200 degrees now in some spots. I checked the basement ceiling below & didnt feel heat, but it's a finished basement so I cant tell if the sub floor is getting hot. Since the R value of the ember pad is zero, wouldnt that 200 degrees transfer to the floor below? Im surprised such a big stove doesnt require thermal protection below. Im wondering if others would be concerned if they had a similar situation.
     
  12. Ashful

    Ashful
    Expand Collapse
    Minister of Fire

    Joined:
    Mar 7, 2012
    Messages:
    8,620
    Likes Received:
    3,586
    Loc:
    Philadelphia
    Many, many threads on this subject... and many academic papers on the same. The one thing that's been learned is that long-term exposure to heat as low as 150F to 200F can significantly lower the combustion temperature of wood. There are many sources pointing to numbers significantly lower than your 572F.

    I suggest you read this thread, as well as the papers to which it refers: http://www.hearth.com/talk/threads/clearances-to-combustibles-theory.102329/
     
    Collapse Signature Expand Signature
  13. cc rangeley

    cc rangeley
    Expand Collapse
    New Member

    Joined:
    Jan 7, 2013
    Messages:
    37
    Likes Received:
    0
    My temp is near 200F... I am trying to understand if that is "normal" for my Rangeley (for which Jotul requires ember protection only) or if my stove is malfunctioning, in which case Im not sure if I ask my installer or the dealer or Jotul for help.
     
  14. Ashful

    Ashful
    Expand Collapse
    Minister of Fire

    Joined:
    Mar 7, 2012
    Messages:
    8,620
    Likes Received:
    3,586
    Loc:
    Philadelphia
    200F on any combustable would be cause for concern... but this is the top of your floor protection, I'm assuming the combustable floor below is somewhat cooler. Can you describe the construction of the floor protection?

    My Jotuls never get the floor temp in front above 100F, but those are well-sunk stone floors. It would be interesting to see what a piece of sheet metal laying on the floor in front of the stove would get to, certainly higher than 100F, but I do agree with your concern... 200F on the floor sounds awful high for an ember-only stove.
     
    Collapse Signature Expand Signature
  15. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,196
    Likes Received:
    7,340
    Loc:
    South Puget Sound, WA
    What temps are you running the stove at? If you are concerned about the hearth pad temps, improve the hearth. The factory requirements are just the minimums. There's no harm if you want to exceed them.
     
    Collapse Signature Expand Signature
  16. KaptJaq

    KaptJaq
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 31, 2011
    Messages:
    703
    Likes Received:
    339
    Loc:
    Long Island, NY
    200° is hot for under that stove. How hot are you running the stove? Stove top temperature, flue temp? Is the bottom heat shield installed? This ships in a separate box and must be attached at installation. With the bottom heat shield the stove needs only ember protection. Without the bottom heat shield it must be on a solid concrete floor over earth only. Is the ash pan door closed and locked?

    KaptJaq
     
    Collapse Signature Expand Signature
  17. cc rangeley

    cc rangeley
    Expand Collapse
    New Member

    Joined:
    Jan 7, 2013
    Messages:
    37
    Likes Received:
    0
    The floor protection is made by aj hearth originals for jotul products. Jotul specifies that the stove needs only a type 1 ember pad. I understand I can add more protection but I'm just wondering if what m experiencing is anticipated by jotul and considered normal in which case I wouldn't add more protection.
     
  18. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,196
    Likes Received:
    7,340
    Loc:
    South Puget Sound, WA
    What temperature are you running the stove at? Where are you reading the 200F?
     
    Collapse Signature Expand Signature
  19. KaptJaq

    KaptJaq
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 31, 2011
    Messages:
    703
    Likes Received:
    339
    Loc:
    Long Island, NY
    Jotul specifies Type 1 only if the bottom heat shield is installed. Otherwise it is poured concrete over earth.
     
    Collapse Signature Expand Signature
  20. cc rangeley

    cc rangeley
    Expand Collapse
    New Member

    Joined:
    Jan 7, 2013
    Messages:
    37
    Likes Received:
    0
    Running stove between 400-500 degrees. It's hot under the stove in the rear primarily
     
  21. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,196
    Likes Received:
    7,340
    Loc:
    South Puget Sound, WA
    He has the bottom heat shield. That's why the original question and why I am asking where he is reading 200F.
     
    Collapse Signature Expand Signature
  22. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,196
    Likes Received:
    7,340
    Loc:
    South Puget Sound, WA
    Is the stove rear exit single wall pipe? How are temps in front of the stove glass on the hearth pad?
     
    Collapse Signature Expand Signature
  23. cc rangeley

    cc rangeley
    Expand Collapse
    New Member

    Joined:
    Jan 7, 2013
    Messages:
    37
    Likes Received:
    0
    Rear exit double wall pipe. Temp on hearth in front by glass is cool. It looks to me like bottom heat shield is in.
     
  24. MasterMech

    MasterMech
    Expand Collapse
    Guest

    Bottom heat shield on the Rangeley is just a piece of sheet metal that is usually installed after the stove is uncrated. Very visible while the ash pan door is open. Mine is pretty cool under there, but I've never measuered the temps. I also have a top vent, double-wall setup so that may be why I get little to no heat under the rear of the stove as well.

    Pictures of your setup would be helpful. Close-ups of the bottom of the stove and the stovepipe where it meets the stove would be great.
     
    northwinds likes this.
  25. begreen

    begreen
    Expand Collapse
    Mooderator
    Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    59,196
    Likes Received:
    7,340
    Loc:
    South Puget Sound, WA
    That's interesting. I'm wondering if a simple shield could be fabricated for the flue collar extending under the horiz. section of the double-wall? To make one I would use a 1' section of inexpensive 6", black, snaplock stove pipe mounted on spacers. Cost would be under $5.
     