So we have another burn ban in town and these always make me think about my alternative heat sources.
For backup heat I have the little 220 volt cadet style wall heaters in each room with their own stats. They are each fed by a 20 amp 220 circuit and 12/2 romex wire. The house has no ductwork and is single story with good attic access.House is only 1700 SF.
I don't have good access to my panel to add more circuits but am considering heat pump options. I did run one 30 amp 220 volt circuit into the attic on 10/3 wire for a future well or maybe a heat pump. So can modern heat pumps be powered with the 30 amp circuit? Can the 20 amp circuits be used after abandoning the wall heaters?
Any other ideas for good heat from those 20 amp circuits. Mini splits are uncommon in my area and the house is 65 feet long. Standard heat pumps are common.
For backup heat I have the little 220 volt cadet style wall heaters in each room with their own stats. They are each fed by a 20 amp 220 circuit and 12/2 romex wire. The house has no ductwork and is single story with good attic access.House is only 1700 SF.
I don't have good access to my panel to add more circuits but am considering heat pump options. I did run one 30 amp 220 volt circuit into the attic on 10/3 wire for a future well or maybe a heat pump. So can modern heat pumps be powered with the 30 amp circuit? Can the 20 amp circuits be used after abandoning the wall heaters?