Had the liberty cruising yesterday at 750 and flue temp of 400 and got out my new toy(IR Thermometer) and took the surface temp of the drywall right behind the stove pipe and the hottest place I could find was 190. Stove is 11 inches from the wall, but the stove pipe is only 15 inches instead of 18 (single wall pipe by the way). Been this way ever since the house was built 18 years ago and so far so good. Probably going to put heat sheild on it over the summer. Just wanted to know if anyone thinks that is too hot for drywall.
Yes, 190°F is too hot for drywall.
Due to having heat issues on my own fireplace I talked to Doug at the USG Drywall technical department.
He said as per the spec sheets on their web site the max continuous temperature exposure is 125°F max. for all USG drywall products including type X and type C drywall.
I find it hard to belive that no one seems aware of this and installers all over the country routinely install drywall in area's that are too hot for it. It won't burst into flame but it won't retain it's fire rating either after extended exposure to elevated temperatures.
PDF specs.
http://www.usg.com/content/dam/USG/...s-regular-firecode-cores-submittal-WB1473.pdf
The USG rep indicated that "temperatures over 125°F are not an appropriate use of this product" and such exposure will degrade the fire rating due to calcination (removal of water) of the gypsum.
Calcination renders drywall unable to properly withstand a fire event because the embedded water is already consumed ahead of time. Calcination occurs as the embodied water of the gypsum material is driven off rendering the board mechanically and thermally unstable. Strength decreases linearly with elevated temperatures and completed calcination is observed with temperatures as low as 125C.
see link
MECHANICAL PROPERTIES OF GYPSUM BOARDAT ELEVATED TEMPERATURES
http://www.fpl.fs.fed.us/documnts/pdf2003/crame03a.pdf
That document has a lot of detail such as:
Chemically combined water is expelled by the gypsum board between 100°C and 125°C, reducing the gypsum to plaster of paris with a loss of it's fire rating and structural strength.
Calcination is mostly complete after the gypsum board reaches a temperature of 125°C. The initial high water content provides 90% of the fire-resistance of the panel.
Gypsum board contains approximately 21% water by weight and as calcination occurs the mass of the board is reduced.
Structural Bending strength of drywall is reduced linearly starting at 100C to near zero percent remaining at 400°C temp exposure for 1 hour.
After 60 minutes of exposure at 200°C, the loss in modulus of elasticity in the gypsum matrix is essential complete (lost) with adhesion to the reinforcing glass fibers the only remaining component contributing to it's strength at that point.