length of baseboard

sixroses Posted By sixroses, Mar 19, 2008 at 6:49 AM

Thread Status:
Not open for further replies.
  1. sixroses

    sixroses
    Member 2.
    NULL
    

    Jan 31, 2008
    70
    0
    Loc:
    alaska
    I have 6 ft of baseboard in my kitchen area. The temp is usually 5* cooler than the living room which is on the same heat loop. Could I double the baseboard in the kitchen area without adverse affects on the next room down the line( a 12x12room). There is no real good way to add baseboard exept by adding a "t" to the original and running a second line directly above the first.? Would this increase the out put??
     
  2. mtfallsmikey

    mtfallsmikey
    New Member 2.
    NULL
    

    Nov 27, 2007
    149
    0
    Loc:
    Mt. Falls Va.
    How much BB (total) is on this loop? What size pipe is feeding it? Rule of thumb: around 67' total on each loop. Around 600 BTU/ft. at 180-190 deg., depending on mfr. spec. Might be as easy as tying it in series with the other.
     
  3. Nofossil

    Nofossil
    Moderator Emeritus 2.
    NULL
    

    Oct 4, 2007
    3,601
    67
    Loc:
    Addison County, Vermont
    If the thermostat is in the living room, you might be able to increase the kitchen temperature by partially closing the louver on the living room baseboards. The living room temp will stay the same, but a higher percentage of the heat will go to the kitchen.
     
  4. Vtgent49

    Vtgent49
    New Member 2.
    NULL
    

    Jan 15, 2008
    102
    0
    Loc:
    Central VT
    You might consider a kick space heater under the cabinets. They help make up for the reduced wall space/baseboard in the kitchen. It involves a fan however, so another moving part to cause trouble. Mine's just in series with the main BB pipe.

    Al
     
  5. Eric Johnson

    Eric Johnson
    Mod Emeritus 2.
    NULL
    

    Nov 18, 2005
    5,875
    147
    Loc:
    Central NYS
    I have a toe-kick heater under the sink in the kitchen. I was going to tear it out, but one nice thing is that when the fan kicks on first thing in the morning, you know your boiler is up to temp.
     
  6. Jersey Bill

    Jersey Bill
    Member 2.
    NULL
    

    Jan 21, 2008
    132
    0
    Loc:
    Central NJ
    you could replace the baseboard with a convector for more output.
    Yes, the next device down the line will see cooler water.
     
  7. sixroses

    sixroses
    Member 2.
    NULL
    

    Jan 31, 2008
    70
    0
    Loc:
    alaska
    I am not familar with a convector. Please explain....
    Steve
     
  8. Jersey Bill

    Jersey Bill
    Member 2.
    NULL
    

    Jan 21, 2008
    132
    0
    Loc:
    Central NJ
    A convector is similar to a radiator. They are usually box shaped, maybe 24 " tall, 4-6" deep. There is no fan, the air circulates by convection. Some sit in front of a wall, or they could be fully or partially recessed.
    here is a link to the Trane models.

    http://www.trane.com/Commercial/Uploads/Pdf/1087/finprc005en.pdf

    They will output more than a baseboard because they are taller and the light warm air heated by the fintube wants to flow more because of the vertical stack effect.

    Another option is to use a wall radiator.
    http://www.runtalnorthamerica.com/residential_radiators/wallpanel-vlx-radiators.html
    these come in any size that you like.
     