ewdudley
Minister of Fire
Never mind.
I think you're right that it's just a matter of insuring that the neck of the safety vent is higher than the cistern level such that it is certain that water would rather flow through storage circuit and not 'pump over' into the cistern.
If the pump might have to choose between the safety vent and a failed-closed malfunctioning zone valve you would want to design for that, but a 1.5 inch circuit over to Tankzilla and back can't have much static head equivalent even at 25 gpm.
I think all you have to do is compute the worst case head the pump could develop at the point from which you would prefer to plumb the safety vent and set the goose-neck of the safety high enough above the highest possible cistern level to overcome that and you're done.
Cheers --ewd