Question about Nofossil's simplest pressurized storage design

Grovenburg Posted By Grovenburg, Nov 25, 2012 at 4:03 PM

  1. Grovenburg

    Grovenburg
    Member 2.
    NULL
    

    Dec 9, 2011
    50
    0
    Loc:
    timangelaryan@comcast.net
    I really like this simple design but have a question: When the load circulator calls for heat and the boilers are cold, the water goes in the bottom and out the top of storage. How does the water keep from circulating through the boilers as well?

    I'm sure this is simple and I'm just missing something. thanks.
     
  2. Gasifier

    Gasifier
    Minister of Fire 2.
    NULL
    

    Apr 25, 2011
    3,152
    794
    Loc:
    St. Lawrence River Valley, N.Y.
    My circulators, Taco 007, have an integrated flow check (IFC) built into them. Oops, I forgot to add that I have several circulators. When the zone circs are calling and the boiler is cold the boiler/primary loop circ is off at that time. So it draws from the tank and returns to the tank.
     
  3. Grovenburg

    Grovenburg
    Member 2.
    NULL
    

    Dec 9, 2011
    50
    0
    Loc:
    timangelaryan@comcast.net
    Do most circulators have IFC's? I have Grundfos 3 speeds and the check valves are in.
     
  4. Gasifier

    Gasifier
    Minister of Fire 2.
    NULL
    

    Apr 25, 2011
    3,152
    794
    Loc:
    St. Lawrence River Valley, N.Y.
    I do not know the answer to your question about if your Grundfos 3 has an IFC.

    How many circulators do you have in the system? If your boiler is cold then the circulator for it will be off, I think that will prevent flow going through your boiler. Hopefully someone else will chime in and make sure I am correct about that.
     
  5. 2.beans

    2.beans
    Minister of Fire 2.
    NULL
    

    Mar 22, 2008
    525
    4
    Loc:
    new hampshire
    If you're saying that you're Grondfos pumps have check valve installed them I would say there are flow check pump. Without a part number or picture I can't say 100%.
     
  6. Grovenburg

    Grovenburg
    Member 2.
    NULL
    

    Dec 9, 2011
    50
    0
    Loc:
    timangelaryan@comcast.net
  7. Grovenburg

    Grovenburg
    Member 2.
    NULL
    

    Dec 9, 2011
    50
    0
    Loc:
    timangelaryan@comcast.net
  8. goosegunner

    goosegunner
    Minister of Fire 2.
    NULL
    

    Oct 15, 2009
    1,382
    101
    Loc:
    WI
    Unless you removed the white plastic check valve from the discharge side it has a check valve.

    gg
     
  9. Nofossil

    Nofossil
    Moderator Emeritus 2.
    NULL
    

    Oct 4, 2007
    3,556
    60
    Loc:
    Addison County, Vermont
    Two things:
    1. The flow check in the boiler circ provides a bit of reluctance - need enough pressure to crack the check valve
    2. The near tank plumbing should be arranged so that the preferred flow direction is through the tank. Hydrostatically speaking, the boiler loop should be a close approximation of closely spaced tees such that there is virtually no flow-induced pressure drop between the tees that connect the wood boiler to storage
     
  10. BravoWhiskey

    BravoWhiskey
    New Member 2.
    NULL
    

    Sep 6, 2012
    32
    4
    Loc:
    NY Southern Tier
    The wood boiler return mixing valve will not flow to load if mixing valve is cool. If using storage for power fail cooling then need mixing valve bypass and siphon circuit. Load circulator won't draw cool water from boiler if it has hot water right there at the top of the storage tank on account of hot water rises.
     