    I thought all EPA stoves have a 15' min. height because that is the EPA testing height. Is this not true?

    Helpful Sponsor Ads!





  2. brenndatomu

    brenndatomu Feeling the Heat

    Joined:
    Aug 21, 2013
    Messages:
    480
    Loc:
    NE Ohio
    See post 32, line 5...EDIT, I'll pull it back up, see next post.
  3. brenndatomu

    brenndatomu Feeling the Heat

    Joined:
    Aug 21, 2013
    Messages:
    480
    Loc:
    NE Ohio
    Lemme see if I can find a link for ya...EDIT, here's one example
    http://www.olympiachimney.com/products/cat/VCAA/VCATSAP/VA_TP0
    Last edited: Oct 12, 2013
  4. dafattkidd

    dafattkidd Minister of Fire

    Joined:
    Dec 11, 2007
    Messages:
    1,537
    Loc:
    Sound Beach, LINY
    Perfect. Thanks. Unfortunately (or fortunately) it has been too warm for burning. I will pick up a piece of four foot galvanized and have it ready for the test burns. If this doesn't work are the draft inducing fans a viable safe option?
  5. STIHLY DAN

    STIHLY DAN Minister of Fire

    Joined:
    Jan 15, 2013
    Messages:
    595
    Loc:
    So NH
    Your chimney may be the problem, Have you looked into the house being in a negative pressure? Exhaust fans, combustion air, dryer. Try opening a window when you open the door to the stove. Also why would you have smoke at all when reloading a burnt down fire? Is your wood actually dry?
  6. Woody Stover

    Woody Stover Minister of Fire

    Joined:
    Dec 25, 2010
    Messages:
    5,586
    Loc:
    Southern IN
    The Keystone manual says 14' but that's with a 7" flue. I'm running 6" at 17'....drafts great.
    The Hearthstone Manchester says 10'....from the floor! _g
  7. Sprinter

    Sprinter Minister of Fire

    Joined:
    Jul 1, 2012
    Messages:
    1,909
    Loc:
    SW Washington
    Yeah, I think that's just a suggested minimum, and probably a good rule of thumb, but mine is only 13' and drafts okay (not great, but okay). Some stoves seem to "breathe" better than others.
  8. begreen

    begreen Mooderator Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    48,038
    Loc:
    South Puget Sound, WA
    Some stoves definitely breath easier than others. Cat stoves that don't rely on secondary air can often get along with a bit less chimney than secondary burners. The design of the secondary intake manifold plays a major part. If it is narrow and/or has a long path with 90 degree turns then it is going to require stronger draft to work well. That is my theory as to why the PE stoves breath easier. They have a large rectangular secondary tube in the back that goes straight up into the large baffle plenum. That is much less restrictive than a stove which has a longer secondary manifold with a couple right angle turns and say a 1" tube intake.

    That should not fault a good secondary burner. With a decent height chimney they can perform very well. Case in point would be the Englander 30NC which is an exceptionally clean burning stove.
  9. dafattkidd

    dafattkidd Minister of Fire

    Joined:
    Dec 11, 2007
    Messages:
    1,537
    Loc:
    Sound Beach, LINY
    My wood is ok. That's not the issue. My house is pretty drafty so I doubt that it's negative pressure. In fact I've tried loading with a window open and no help. I'm pretty positive it's the chimney height or the offset box, or both.
  10. Dustin

    Dustin Feeling the Heat

    Joined:
    Sep 3, 2008
    Messages:
    392
    Loc:
    Western Oregon
    What type of stove? I get smoke spillage each and every time I open the door to my quad. No matter what I do.

    25 feet of flex on an interior chimney. Some stoves like putting a little smoke in the room I think
  11. dafattkidd

    dafattkidd Minister of Fire

    Joined:
    Dec 11, 2007
    Messages:
    1,537
    Loc:
    Sound Beach, LINY
    I have an Osburn 2400 insert. It's a basic unit. No bells and whistles just a beast. There are other members on the forum with the same unit who do not share this experience. It's not the stove. It's the chimney system.
  12. Sprinter

    Sprinter Minister of Fire

    Joined:
    Jul 1, 2012
    Messages:
    1,909
    Loc:
    SW Washington
    I believe the math is right. I've read other sources that confirm that kind of relationship. So if you go ahead and add 3 ft, you probably will get about 25% more draft which more than likely will solve your problem. Every additional increase in height, though, will have a lesser affect.

    Do what others have suggested and temporarily add some cheap stovepipe. That will tell the tale.
  13. BCC_Burner

    BCC_Burner Feeling the Heat

    Joined:
    Sep 10, 2013
    Messages:
    306
    Loc:
    Wasatch Front: 7800'
    I think adding height is the best option here. Also, don't overlook the basics to help improve things a bit before you add height. Open the primary air all the way for 30-60 seconds before opening the door, and open the door slowly. I usually leave mine cracked open just slightly for a couple seconds before slowly opening it the rest of the way. Being vigilant about those two steps really reduced smoke spillage in my experience.
  14. begreen

    begreen Mooderator Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    48,038
    Loc:
    South Puget Sound, WA
    Something doesn't sound right there. Did the liner get flattened a lot to pass thru the damper? Is the baffle all the way to the rear of the stove? Has the baffle been checked to see if there is a mound of soot sitting directly under the flue collar? Is the cap screen clean?
  15. oldspark

    oldspark Guest

    Yea 25 feet of chimney should not spill smoke back into the room, I only have 18 feet and it never spills back into the room and it did not with the old chimney and old stove.
  16. Charles1981

    Charles1981 Minister of Fire

    Joined:
    Feb 19, 2013
    Messages:
    510
    Loc:
    Michigan
    I have a 27 foot 6 inch chimney. My masonry chimney is completely interior in the middle of the home in the basement. I have 6 inch SS pipe all the way up (my installer said because I have a interior, clay lined masonry chimney I had no need for insulated double walled pipe.

    I have it hooked up to a encore 2 in 1.

    From some other posts drafts have been a significant issue for people with this stove. I am wondering if because of the height, location, and diameter of chimney/liner this is one reason the stove has been performing as it supposed to? Seems like i have an ideal situation for any stove...unless there was a problem with too much draft...but I'm not sure how to tell if I have too much draft?
  17. dafattkidd

    dafattkidd Minister of Fire

    Joined:
    Dec 11, 2007
    Messages:
    1,537
    Loc:
    Sound Beach, LINY
    So for the past two weeks I have been running the unit with a four foot piece of single wall stove pipe attached to the top of my liner. The additional four feet has slightly improved my smoke in your face problem, but not really fixed it. It has to be the offset box. I have a mason coming to my house today to tell me if I can make some adjustments to the masonry to eliminate the offset box.

    I do however like the way my stove runs with the longer chimney. It seems to take off faster, I can pack the splits tighter and have a more complete burn. It looks RIDICULOUS though. Holy cow it looks terrible. I'll post a picture just for kicks.

    I'll update the thread after speaking to the mason today. For the record: The mason who is meeting me at my house today has done a ton of work for my company (we build very high end homes in the Hamptons). So his opinion holds a lot of weight in my book.
    Last edited: Dec 11, 2013
  18. dafattkidd

    dafattkidd Minister of Fire

    Joined:
    Dec 11, 2007
    Messages:
    1,537
    Loc:
    Sound Beach, LINY
    Ok. Bad news. There are some options, but they are pretty invasive and expensive. My last hope is this: The fireplace has a steel box with vents that was most likely installed in the 70s or early 80s. Based on the measurements it looks like behind this steel box is a full masonry fireplace. The only way to tell is to cut out the steel. If I do this, I can slip my insert further back into the fireplace eliminating the need for an off set box. I think the steel is most likely too think to cut with a sawzall. We think we probably need to hit it with a plasma cutter.

    Can anyone confirm that the steel boxes installed in the 70s and early 80s were too thick to be cut with a sawzall?
  19. Jags

    Jags Moderate Moderator Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    15,026
    Loc:
    Northern IL
    I have cut 1/4" plate with a sawsall. Goes faster than you think.
  20. MDFisherman

    MDFisherman Member

    Joined:
    Sep 17, 2012
    Messages:
    132
    Loc:
    So. MD
    Or a angle grinder with a cutting wheel will make short work of that for sure.
  21. dafattkidd

    dafattkidd Minister of Fire

    Joined:
    Dec 11, 2007
    Messages:
    1,537
    Loc:
    Sound Beach, LINY
    Good to hear.

    The plan would be: Disconnect the liner from the insert. Slide insert out of fireplace. Cut the steel box out. Pray that it is fully masonry behind that. Slide my insert deeper into pocket of the fireplace so the exhaust passes the lintel. Directly connect the liner to the insert. Light a massive fire with no smoke spillage, and drink a beer.

    Most likely the actual outcome: Attempt to disconnect liner from insert, but the tight squeeze between the top of the insert and the lintel lead me to have to sawzall the God forsaken off set box. Pullout insert and damage my hearth. Begin to attempt to sawzall steel box. Break/destroy several sawzall blades. Run out buy ore sawzall blades. Burn out sawzall. Engage in raging break down. Run to nearest fireplace supplier purchase offset box. Connect offset box to liner. Slide insert back into place, connecting offset box as the I shimmy the insert back into place. Light fire. Get face full of smoke. Drink beer. Nod head repeatedly in disappointment. Post results on Hearth.com
    nola mike likes this.
  22. Jags

    Jags Moderate Moderator Staff Member

    Joined:
    Aug 2, 2006
    Messages:
    15,026
    Loc:
    Northern IL
    You are quite the optimist. I would expect the outcome to be much worse.:p
  23. brenndatomu

    brenndatomu Feeling the Heat

    Joined:
    Aug 21, 2013
    Messages:
    480
    Loc:
    NE Ohio
    ;lol keepin it real this morning...
  24. mellow

    mellow Resident Stove Connoisseur

    Joined:
    Jan 19, 2008
    Messages:
    3,191
    Loc:
    Salisbury, MD
    Mine had another steel back behind the steel back that you are cutting out to allow the heat to move behind it for the heatilator vents.
  25. oconnor

    oconnor Minister of Fire

    Joined:
    Nov 20, 2005
    Messages:
    1,060
    Loc:
    Nova Scotia
    Instead of cutting the entire fireplace out, can you just cut the fireplace throat so you can get a better angle to the liner?