Tarm Solo 40 running high pressure

Post in 'The Boiler Room - Wood Boilers and Furnaces' started by Reggie Dunlap, Jan 2, 2013.

  1. Reggie Dunlap

    Reggie Dunlap
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 13, 2005
    Messages:
    314
    Likes Received:
    1
    Loc:
    Northern Vermont
    I've had my Tarm for 5 trouble free winters now, hooked up to 750 gallons of storage. Today it started running at 20-25 PSI for some reason, it's always been in the 10-15 PSI range. Nothing else has changed that I know of, other than it's 15 below right now.

    Any ideas or thoughts would be appreciated.
     
    Collapse Signature Expand Signature

    Helpful Sponsor Ads!





  2. Floydian

    Floydian
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 12, 2008
    Messages:
    459
    Likes Received:
    98
    Loc:
    Southwestern VA
    Do you have a bladder expansion tank(s)? That would be the first thing I'd check. Or maybe an autofill gone wacky?

    Noah
     
    Collapse Signature Expand Signature
  3. Reggie Dunlap

    Reggie Dunlap
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 13, 2005
    Messages:
    314
    Likes Received:
    1
    Loc:
    Northern Vermont
    Yes I have an expansion tank. Could be the autofill, I guess I should shut the supply off to it.
     
    Collapse Signature Expand Signature
  4. Reggie Dunlap

    Reggie Dunlap
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 13, 2005
    Messages:
    314
    Likes Received:
    1
    Loc:
    Northern Vermont
    I should also add that my storage is unpressurized.
     
    Collapse Signature Expand Signature
  5. rcollman

    rcollman
    Expand Collapse
    Member

    Joined:
    Dec 13, 2008
    Messages:
    58
    Likes Received:
    1
    Loc:
    Northern NH
    Ditto the cold in Norhtern NH. It is now (noon) a balmy 0 outside up from -16.4 at 7:15 AM.

    And ditto check the autofill. I seem to recall that happened to us in the first season. I got a small bucket with a handle. Turned off the autofill, and drew off some water out of the system next to my backup boiler. Alternatively you should have a pressure relief value, with a handle at the top and a pipe pointed to the floor, or into a drain. It will take less than 2 cups of HOT water out of the boiler to reduce the pressure.

    I think I turned the autofill back on and the pressure did not build up again. Wrote it off to some installation grit keeping the valve open.


    Stay warm!
     
    Collapse Signature Expand Signature
  6. Reggie Dunlap

    Reggie Dunlap
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 13, 2005
    Messages:
    314
    Likes Received:
    1
    Loc:
    Northern Vermont
    Yep, cold here too. 18 below this morning, now around 0.

    I think it is the autofill. I shut it off and drained enough water to bring it down to 15 PSI with the boiler at 180 degrees.

    Thanks for the help.
     
    Collapse Signature Expand Signature
  7. KenLockett

    KenLockett
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 27, 2011
    Messages:
    432
    Likes Received:
    67
    Loc:
    Eastern Upstate NY
    Reggie, did you buy your storage tank from Biomass USA in NH?
     
    Collapse Signature Expand Signature
  8. Reggie Dunlap

    Reggie Dunlap
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 13, 2005
    Messages:
    314
    Likes Received:
    1
    Loc:
    Northern Vermont
    No, I built it out of concrete block with an EPDM pond liner. I wish it was closer to 1000 gallons, but it works great going on 5 years.
     
    Collapse Signature Expand Signature