    Just moved into a house that has a NG Vermont Castings Radiance (no idea how old, but seems clean).

    Starting to get cold this time of year so went through the process of firing it up for the first time. Checked for leaks, fixed a section of dented vent pipe... lit pilot and that stayed on just fine... but once I light the flame I only get a tiny blue flame (turning the adjustment knob only has a very slight effect)

    Flame's hard to photograph, but here's a try.
    https://www.dropbox.com/s/04arco3zg20qbvr/IMG_20131115_214334.jpg

    So I'm a bit perplexed... not enough air?

    Helpful Sponsor Ads!





  2. BrotherBart

    BrotherBart Hearth.com LLC Mid-Atlantic Division Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    27,148
    Loc:
    Northern Virginia
    One of our gas wizards is traveling but hopefully another will pop in with advice.
  3. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
  4. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
    Could it be low pressure? Looking at the meter there are four lines - a 3/4" pipe feeds a range and a hot water heater about 35ft away... then there's a dryer right near the meter (5ft) with 1/2" and there's a 1/2" split off of that dryer line running in the opposite direction about 20-25" to the fireplace...

    EDIT: Just looked at the lines and did some basic math... shouldn't be the supply...

    https://www.dropbox.com/s/x11uhzndu8cl0o3/Screenshot 2013-11-16 12.28.05.png
    Last edited: Nov 16, 2013
  5. Fake coal burner

    Fake coal burner Member

    Joined:
    Nov 11, 2008
    Messages:
    222
    Loc:
    Salt Lake City Utah
  6. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
    Just found the manual in the previous owner's belongings, it's a Vermont Castings Radiance RDV40... seems to be older than the current models they have listed on their site.

    The manuals aren't much help - the pilot lights and stays lit, the fire turns on/off, fumes are vented out the wall... no major red flags other than the wimpy flame.

    Guess I might just have to pay someone to come out and take a look at my gas pressures, or at least look at my diagram - I've got experience with solid fuel stoves, but a bit of an amateur when it comes to natural gas systems.
  7. DAKSY

    DAKSY Patriot Guard Rider Staff Member

    Joined:
    Dec 2, 2008
    Messages:
    4,889
    Loc:
    Averill Park, NY, on Burden Lake II...
    Do you feel confident enough to remove the burner pan? What you are seeing may just be a blocked gas line. Damned spiders get behind the burner orifice & build a nest that almost completely blocks the flow thru the gas line. That's where I'd look before calling a service tech...
  8. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
    Yeah , seems simple enough. Is it a matter of cleaning out the orifices themselves? should I remove them? (I think there are two)

    Is there any simple way to tell that it's a supply line issue before having the plumber come out and run some new lines? are these the symptoms of low volume?
    Last edited: Nov 17, 2013
  9. DAKSY

    DAKSY Patriot Guard Rider Staff Member

    Joined:
    Dec 2, 2008
    Messages:
    4,889
    Loc:
    Averill Park, NY, on Burden Lake II...
    Yes, but you'll need a manometer. You can tap into the gas port on the front of the gas valve IF there is one. If you don't know, you'd have to post a pic of the front of the valve in order for me to tell...
  10. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
    [​IMG]
    I can take a photo of my actual valve if this isn't good enough — but this is the same exact valve. I assume those silver cylinders under the knobs are the ports... or are those adjustment screws?
  11. DAKSY

    DAKSY Patriot Guard Rider Staff Member

    Joined:
    Dec 2, 2008
    Messages:
    4,889
    Loc:
    Averill Park, NY, on Burden Lake II...
    I can't see the labelling, but if it says PILOT that's the pilot adjustment screw. If it says IN or OUT those are the pressure ports...In will tell you the gas pressure to the valve. Out will tell you the gas pressure to the burner...
  12. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
    Yeah the pilot adj screw is above the electrical contacts on the left there (hard to see in that photo)

    Great, so would just about any manifold pressure testing kit work here?

    A friend of mine has one of these, for example http://www.amazon.com/gp/product/B0...pf_rd_t=101&pf_rd_p=1630083462&pf_rd_i=507846
  13. DAKSY

    DAKSY Patriot Guard Rider Staff Member

    Joined:
    Dec 2, 2008
    Messages:
    4,889
    Loc:
    Averill Park, NY, on Burden Lake II...
    That'll work just fine...
  14. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
    So this might be one for the record books...

    the inlet pressure is fine at about 10 inch WC (acceptable range is 5.5 - 14) - but the pressure at the burner is rated way too high, around 7-9 WC (depending on lo-hi knob adjustment - should be 3.5)... did these knuckleheads run a natural gas line to a stove adapted for LP? Is there something else that would cause this issue?

    Might just have to sell this thing in that case, doubt I can still get the conversion kit for a model this old.
    Last edited: Nov 23, 2013
  15. DAKSY

    DAKSY Patriot Guard Rider Staff Member

    Joined:
    Dec 2, 2008
    Messages:
    4,889
    Loc:
    Averill Park, NY, on Burden Lake II...
    Sounds like it's the regulator. You should be able to get one, since they're made for the valve & not for the stove model...Take the model & serial number off the valve & talk to your local hearth shop or maybe an industrial supply place...
  16. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
    Any chance it's been converted for LP use? just wondering because those pressures seem to be pretty close to the rated LP pressures.

    I'm guessing if I find the serial numbers and look those up or ask a local hearth shop they'd be able to tell me?
  17. DAKSY

    DAKSY Patriot Guard Rider Staff Member

    Joined:
    Dec 2, 2008
    Messages:
    4,889
    Loc:
    Averill Park, NY, on Burden Lake II...
    Technically, if your unit was converted by a licensed or certified gas tech, there should be a couple of stickers indicating which kit & the date that it was converted. If it was converted by Joe Homeowner, that may not have happened. Almost all valves are set up for NG from the factory & converted as needed. The serial number will not tell them much, but you can look at the regulator. There should be some numbers or different colored screw heads (Red=LP; Blue = NG)...
  18. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
  19. DAKSY

    DAKSY Patriot Guard Rider Staff Member

    Joined:
    Dec 2, 2008
    Messages:
    4,889
    Loc:
    Averill Park, NY, on Burden Lake II...
    Hmmm. I don't think so, because there is a "1/2 PSI" stamped on that feature & that's incoming NG pressure...
  20. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
    Hm ok, I think I'm probably at the limit of what can be done without having a technician come in and take a look! Thanks again.
  21. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
  22. DAKSY

    DAKSY Patriot Guard Rider Staff Member

    Joined:
    Dec 2, 2008
    Messages:
    4,889
    Loc:
    Averill Park, NY, on Burden Lake II...
  23. earthwindfireplace

    earthwindfireplace New Member

    Joined:
    Nov 15, 2013
    Messages:
    13
    Loc:
    United States
    Not a word about orifices in the manual at all — I did remove them and clean them though. I'm stuck on the idea that this is an LP appliance that someone tried to hook up to NG without converting it... going to see if I can get someone in to service it this week to find out for sure.