Water pressure and efficiency

stoney28 Posted By stoney28, Nov 8, 2013 at 4:09 PM

Thread Status:
Not open for further replies.
  1. stoney28

    stoney28
    Member 2.
    NULL
    

    Oct 12, 2008
    59
    2
    Loc:
    Northern NY
    I've got an EKO 40 with 500 gallons of storage. Earlier this year I had a leak in the boiler which has since been welded. I've been cautious about running up the pressure since then, so I'm only running the pressure (at full temp 180F) at about 15 to 18 psi. Will this affect the efficiency of the boiler? Are there any other problems that could come up?
     
  2. BoilerMan

    BoilerMan
    Minister of Fire 2.
    NULL
    

    Apr 16, 2012
    1,717
    325
    Loc:
    Northern Maine
    Short answer is no. Water pressure has no effect on heat transfer efficiency, as long as there is no boiling. Some boilers (Garn, Empyre, etc.) are open systems meaning they are vented to atmosphere at a high point and run at zero pressure. 15-18 psi is a good place to be at full temp.

    TS
     
  3. stoney28

    stoney28
    Member 2.
    NULL
    

    Oct 12, 2008
    59
    2
    Loc:
    Northern NY
    Thanks
     
  4. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    6,645
    1,145
    Loc:
    Nova Scotia
    I keep my pressures fairly low - around 6-8 cold to 12 hot. No issues that I've seen, and I'm circulating around two storeys.
     
  5. stee6043

    stee6043
    Minister of Fire 2.
    NULL
    

    Aug 22, 2008
    2,509
    236
    Loc:
    West Michigan
    Low pressure may not impact the boiler but are your pumps rated to run at a certain pressure? Some brands/models don't like low (perhaps sub 10) pressure.

    My system holds at 12-14 psi cold. 25-26 psi typical max pressure when she's all up to temp.
     
  6. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    6,645
    1,145
    Loc:
    Nova Scotia
    Think I'm Ok there. Alpha specs. min 0.75psi @ 167°, 4.06 psi @ 194°. Mine is on my return line so would never, or very rarely, see much above 167°. If it did my system would have to be pretty well up to temp which would be in the 12psi range.

    I did have issues with getting all the air out of my upstairs zones when I first started up with the new boiler, lots of frigging around there with hoses going here & there - but once I got those purged haven't had any more air problems.
     