    I have 4 heating zones controlled by zone valves. I also have a 40 gallon superstor with it's own zone valve. I'd like to make the superstor have priority over the heating zones. Is there a simple inexpensive way to do this?
    #1

    Helpful Sponsor Ads!



  2. mysticfalcon New Member

    joined: May 9, 2008
    51 posts
    Northern VT
    A taco ZVC control will prioritize the hot water zone.
  3. WoodNotOil New Member

    joined: May 6, 2008
    904 posts
    Northern, Vermont
    Depending on how your system is wired, you could put in an inexpensive relay (like the one I used $8 I think) that interupts the 110vac going to your thermostat controlled relay box(s) that would simply deprive them of electricity if the superstore is on. If you do that, make sure it has a very high Amp rating as it will handle the amp load of at least the 4 pumps probably. If you have seperate feeds you could use multiple relays etc. Once you involve a lot of relays and armored cable, it may be more cost effective to use a commercial product like Mysticfalcon suggested.
  4. chuck172 Minister of Fire

    joined: Apr 24, 2008
    1,011 posts
    Sussex County, NJ
    Yeah, a zone control with priority is probably the best way to go about it. If anything, I'd like to simplify my wiring. It's a rats' nest now.