Just bought a house with an existing 25-PDVC manufactured in 10/2008. Did a simple ash cleaning of the burn pot and only ran about 3 bags of pellets through it before I realized it wasn't right. Black covers the window within 2 hours, luke warm heat, weak flame. Decide to do a complete maintenance cycle on the unit to start fresh. Ash filled everywhere, scrape everything down on the inside, disconnect unit from the flue and its 25-50% full of ash. End up taking the entire flue system off the house and brush and blow everything clean. Exhaust blower was full of soot and ash and convection blower was covered in dust. Fresh air intake screen was 75% clogged up too. My guess is the previous owner didn't do any of the larger cleanings.
But I think root of the problem is the flue venting. When stove was first installed a stud and outlet were in the way of where a simple 45 degree offset would have let the pipe leave the stove and go through the wall but because they moved over to the center of a stud bay they had no choice but to use a 45 degree and a 90 degree right off the bat leaving the stove. It also forced the stove to sit more forward and off center on the tile flooring.
Manual wants 3 feet of vertical rise outside assuming the unit just vents right out the wall with no elbows, he doesn't even have that, he only installed 2 feet of verticals before the 90 and cap. Manual wants an extra 3 feet for every elbow used, so my 90, 45 would mean an extra 6 feet of vertical on top of the 3' for a total of 9'. Well I have a soffit in the way, I can add 1 additional foot of height to get to 3' and still have the required 24'' of soffit clearance but I don't meet the required vertical.
With these stove with an exhaust blower does it help overcome poor flue venting vs natural draft only? I've read that you can get away with it but if power goes out the smoke will want to come back in the house if your flue design is poor and only worked because of the mechanical push.
I don't want to turn the unit as its in the corner. My options are so far this....
1. Open up the wall and move the outlet and cut and box out around the stud so I can use only a single 45 degree elbow to get from the unit to outside. Add the extra 1 foot piece or replace with a single 3' foot piece so I get my 3' of vertical even through with a 45 degree I should be at 6' vertical.
2. Go up and through the eave and the roof, getting the 9' required rise allowing existing elbows and holes through wall to stay.
3. Do step 1 and step 2 since more vertical is better as long as I stay less that 15' so I dont have to go up to 4'' pipe
4. When I do go through the roof I do not want to stop at the required 1 foot higher than the roof as I have solar panels right there and dont want any soot so I would go up higher to at least the peak of the roof which would be about 4 feet of pipe from roof line to get to the height of the peak of the roof so total vertical run in that case would be 9.5' which would give me the vertical required to keep the elbows.
But I think root of the problem is the flue venting. When stove was first installed a stud and outlet were in the way of where a simple 45 degree offset would have let the pipe leave the stove and go through the wall but because they moved over to the center of a stud bay they had no choice but to use a 45 degree and a 90 degree right off the bat leaving the stove. It also forced the stove to sit more forward and off center on the tile flooring.
Manual wants 3 feet of vertical rise outside assuming the unit just vents right out the wall with no elbows, he doesn't even have that, he only installed 2 feet of verticals before the 90 and cap. Manual wants an extra 3 feet for every elbow used, so my 90, 45 would mean an extra 6 feet of vertical on top of the 3' for a total of 9'. Well I have a soffit in the way, I can add 1 additional foot of height to get to 3' and still have the required 24'' of soffit clearance but I don't meet the required vertical.
With these stove with an exhaust blower does it help overcome poor flue venting vs natural draft only? I've read that you can get away with it but if power goes out the smoke will want to come back in the house if your flue design is poor and only worked because of the mechanical push.
I don't want to turn the unit as its in the corner. My options are so far this....
1. Open up the wall and move the outlet and cut and box out around the stud so I can use only a single 45 degree elbow to get from the unit to outside. Add the extra 1 foot piece or replace with a single 3' foot piece so I get my 3' of vertical even through with a 45 degree I should be at 6' vertical.
2. Go up and through the eave and the roof, getting the 9' required rise allowing existing elbows and holes through wall to stay.
3. Do step 1 and step 2 since more vertical is better as long as I stay less that 15' so I dont have to go up to 4'' pipe
4. When I do go through the roof I do not want to stop at the required 1 foot higher than the roof as I have solar panels right there and dont want any soot so I would go up higher to at least the peak of the roof which would be about 4 feet of pipe from roof line to get to the height of the peak of the roof so total vertical run in that case would be 9.5' which would give me the vertical required to keep the elbows.