I have the 3 flashes, on my TUE100, however I don't have 115v at the vent motor nor from the board (obviously). Does the board have a lockout and need to be reset. Or do I have a bad board?
Sorry, n.e.i. I have a dual fuel system. I didn't check the second stage heat for 24v. I'll try that when I get back home. I went ahead and got a board at lunch time just in case.
Sorry, n.e.i. I have a dual fuel system. I didn't check the second stage heat for 24v. I'll try that when I get back home. I went ahead and got a board at lunch time just in case.
!! The switch would measure open with a meter, but the board was sensing closed on startup, my meter was not picking it up. Before starting the furnace, pulled off one side of the pressure switch wire, inducer started, put back on furnace fired up. Replaced pressure switch all is good!! Take care all and have a Happy Thanksgiving