Going to make an assumption here: 900 sq. ft. = 9000 cu. ft. volume - no cathedral ceiling. It takes about .2 btu to raise one cu. ft. of air. one degree. -15 c. is 5 f., so if you want to raise the temperature to, say, 70 deg. f., that is an increase of 65 deg. f., necessitating 117,000 btu.
Englander rates the NC 30 at 75,000 btu, so just to heat the air will require burning at the maximum output for something like an hour and a half. BUT
! You also have to raise the temperature of the furniture, the cabinetry, the interior walls, the frozen tube of toothpaste left last time you were there, everything. And meanwhile the envelope is losing heat continuously - this is what R factor measures, after all. And a maximum output for any stove is tough to maintain for more than about 90 minutes or so.
I am going to guess that to bring the cabin up to 70 degrees will take many hours - five, six, maybe eight. I have a personal comparison, not a great one, but a comparison: My very well insulated, 1300 sq. ft. house in Colorado is set to stay at 40 deg. f. when we are gone. When we need to bring the temperature back up to 65 deg. f. in 0 deg. outside temperatures our 80,000 btu furnace (80% efficient, 64,000 btu output) runs non stop for about two, two and a half hours.
One the other hand, the area immediately around the stove should be pretty comfortable in 90 minutes or less.