8" flue to 6" pipe at ceiling - unsafe?

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

la44

New Member
Hearth Supporter
Dec 1, 2007
5
upstate NY
PLEASE HELP! Vermont CASTINGS EXPERTS OUT THERE! I purchased a Vermont Castings Encore non-catalytic stove three years ago. The most recent chimney sweep told me that it is not "up to code." The flue is oval, 8". The collar and pipes leading up to the ceiling are 8". At the ceiling level the chimney pipe becomes 6". All pipes are double-walled. Can anyone help me understand the specifications on this? What is an 'optional 6" flue collar'? A reversible flue collar? Anyway, it is snowing and the stove is dismantled in my living room. Jury is out, along with fire inspector...
 
yeah, there are several things that nobody here will argue with. reducing a pipe is ALWAYS a no-no. heat build up, gas build up, whatever may happen, you can be assured that it won't have good consequences to take some 500 degree air that's flowing up the chimney and say "hey, hot air, i know you want to ALL move through here, but instead I can only let some of you go at a time."
 
what about running a 6" wood burner into a 8" chimeny pipe at the ceiling?
 
greythorn3 said:
what about running a 6" wood burner into a 8" chimeny pipe at the ceiling?
wouldn't running into a larger pipe slow down the speed of the gasses and then impact draw? I'm not sure. I bet that going larger up by the ceiling is less of a danger and merely presents more of a problem with draft. I mean, when your chimney empties into the world, it's going from 6" to an infinite sized pipe, so as long as your ceiling is super high and you can good a good draft with it, then it should be fine. If your ceiling is 8' and your pipe is running from the top of the stove, then I think you might have problems.
 
Thanks all for your help. I've been getting conflicting opinions on how to fix my problem. The stove calls for 8" pipe from the oval opening. There is an "optional 6" flue collar" that they could install, but wouldn't that prevent safely opening and closing the front doors? I think what has to be done is replace all the stovepipe - from flue to chimney top - to be 8", so that I can safely use the stove, open and close the front doors when necessary, etc. Anybody have a different opinion?

And if I reduced to 6" flue collar, will that affect creosote buildup right in the stove and overall safety?

Since the dealer installed everything, I'm trying to get my ducks in a row to have them fix the problem. I want the safest solution. Thanks again for all your help.
 
Back in the old days when it wasn't against code, we would often reduce an 8 inch flue using an 8-to-7 taper and then a 7-to-6 taper. You cannot argue with code however so if a 6 inch collar is available to bring it up to code, do it. It shouldn't make a difference in your draft and won't cause creosote. Think of the flue gasses as a train. The engine and the caboose both travel at the same speed.
 
LLigetfa said:
Think of the flue gasses as a train. The engine and the caboose both travel at the same speed.
Not if the engine is in the 6" and the caboose is in the 8". In this case the caboose would be dragging ass. :)
 
The point I was trying to make is that the caboose won't travel any faster than the engine.

Back in the days when we used tapered reducers, we theorized that hot gasses expand and the cooling gasses shrink as they rose up from the stove, so their velocity increased only slightly as the pipe narrowed. This was to counteract the theory that slower moving gasses in an 8 inch flue slowed as it rose and cooled which caused it to cool more and slow more until it eventually stalled.
 