See if this helps Franzen.
 

Attachments

  • [Hearth.com] A Fresh Eko 40 with 500 gal Storage Install
    P1060757.webp
    15.5 KB · Views: 520
galvanized is okay in a hydronic system, use a brass fitting if you plan on connecting copper to galv.

But galvanized cannot be used in a glycol system, according to Dow and other glycol manufacturers.

As for the sand bed storage, that was intended to work wirh a solar thermal array. The concept is to start loading the sand bed in the late summer/ fall and flywheel off that stored energy into the winter months. Wisconsin solar guru Bob Ramlow promotes that system in your area.

hr
 
in hot water said:
galvanized is okay in a hydronic system, use a brass fitting if you plan on connecting copper to galv.

But galvanized cannot be used in a glycol system, according to Dow and other glycol manufacturers.

As for the sand bed storage, that was intended to work wirh a solar thermal array. The concept is to start loading the sand bed in the late summer/ fall and flywheel off that stored energy into the winter months. Wisconsin solar guru Bob Ramlow promotes that system in your area.

hr

So how important is it to have brass between Black iron and copper?

I have heard and read so many differing opinions on that what is your suggestion?

I have pressurized and treated water system.
I didn't put brass between mine, should I be planning a change?

gg
 
Pardon my ignorance but aren't most sacrificial anodes made of zinc? do they have adverse effects when they deteriorate or are they never in the boiler water stream?
 
Yes ,the bypass is just a ball valve and it looks like your danfoss should swap places with the "T" directly above it.
Does that lower line that the danfoss is in now connect to the bottom of the storage tank?
 
SO just making sure i have this right
looking at the Danfoss.. The Circle on the Valve is the Suppy, the triangle will the return from tank. and the square is the return to the boiler. If i blow air through the valve, the air goes through the circle to the square cause its cold. Correct???????????.........
 

Attachments

  • [Hearth.com] A Fresh Eko 40 with 500 gal Storage Install
    danfoss.webp
    23 KB · Views: 551
Well got it all put back together. Pressure tested two tiny copper leaks, and one tiny tank weld leak..... getting ready to fire her up!!!!!
 

Attachments

  • [Hearth.com] A Fresh Eko 40 with 500 gal Storage Install
    boiler 2.webp
    12.6 KB · Views: 535
Well that one leak caused another caused another and another. A day of chasing leaks and She is sitting at 15 psi with no drips. Is it normal that with all this work, i am little afraid to fire it up......:) YICKS....
 
Well I went for it.. Pretty pleased so far. After starting at 49.1 degrees she warmed up the top nicely. The bottem took a while but it is catching up pretty quickly now!!!! Going to drain it in the morning and start over. Perfect timing snowing up here in northwest wisconsin....








Not to bad after a 5 hour burn with low quality wood ie, dry Poplar, Birch, Maple, Tamarack
 

Attachments

  • [Hearth.com] A Fresh Eko 40 with 500 gal Storage Install
    temp1.webp
    41.2 KB · Views: 456
  • [Hearth.com] A Fresh Eko 40 with 500 gal Storage Install
    temp2.webp
    28.3 KB · Views: 455
  • [Hearth.com] A Fresh Eko 40 with 500 gal Storage Install
    temp3.webp
    36.6 KB · Views: 466
Nice Franzen105. Keep us posted. I gotta get me a few of those digital meters and sensors. Pretty slick.
 
The Orange housing is a hot water filter.
After only a few hours heating my large sand mass system the floor in the house is already heating up!!! Saweet.........:)
 
All right! Good deal. Keep us posted man. Glad to hear the heat is coming through! :coolcheese:
 
You use that to choke back the flow from the bypass line. If you have temp gauges on the return before the danfoss and the mixed after the danfoss you can close it down as your tank heats some. My initial fire was the only time I had it open very far. It is close to closed now.

gg
 
Isn't the Danfoss supposed to output the right temperature? I thought that was its function - not quite understanding why a manual valve would have to be added to make it work right.
 
maple1 said:
Isn't the Danfoss supposed to output the right temperature? I thought that was its function - not quite understanding why a manual valve would have to be added to make it work right.

The water flowing through the bypass line is what causes thr thermostat in the Danfoss to actuate. Circulator activates on return pipe and initially pumps water through the bypass line because at that point in time the automotive thermostat is closed. When the water flowing through the bypass line reaches 140 °F or whatever value you installed it flows on to the sensor part (bulb) of the thermostat and causes it to open. Colder water from your heating loop starts entering the boiler mixing with the warmer recirculating water.

Now you have two sources flowing, both tempering each other which more than likely will not allow the thermostat to open much or even possibly close again until the flow from the bypass warms the bulb. When the return water from the system reaches your desired temperature, in my case 140 °F the bulb will sense it and stay open, allowing circulation from the heating loop.

The variable restriction (ball Valve) placed in the bypass line is to limit the flow to your needs. Partially closing it restricts circulation through the loop, allowing more flow from the heat loop. I my case I hit the sweet spot on the ball valve about three years ago and haven't touched it since. Some of it has to do with my set points for circulator actuation but mostly has to do with my heat load or how much heat my flatplate exchanger can transfer into my unpressurized storage tank.

Wanna see how it works. Close the bypass valve completely and the Danfoss will never open.
 
Fred61 said:
maple1 said:
Isn't the Danfoss supposed to output the right temperature? I thought that was its function - not quite understanding why a manual valve would have to be added to make it work right.

The water flowing through the bypass line is what causes thr thermostat in the Danfoss to actuate. Circulator activates on return pipe and initially pumps water through the bypass line because at that point in time the automotive thermostat is closed. When the water flowing through the bypass line reaches 140 °F or whatever value you installed it flows on to the sensor part (bulb) of the thermostat and causes it to open. Colder water from your heating loop starts entering the boiler mixing with the warmer recirculating water.

Now you have two sources flowing, both tempering each other which more than likely will not allow the thermostat to open much or even possibly close again until the flow from the bypass warms the bulb. When the return water from the system reaches your desired temperature, in my case 140 °F the bulb will sense it and stay open, allowing circulation from the heating loop.

The variable restriction (ball Valve) placed in the bypass line is to limit the flow to your needs. Partially closing it restricts circulation through the loop, allowing more flow from the heat loop. I my case I hit the sweet spot on the ball valve about three years ago and haven't touched it since. Some of it has to do with my set points for circulator actuation but mostly has to do with my heat load or how much heat my flatplate exchanger can transfer into my unpressurized storage tank.

Wanna see how it works. Close the bypass valve completely and the Danfoss will never open.

I must be slow, I'm still not understanding it. Does the (hot) bypass loop actuate the thermostat, or the (colder) return line? The bolded above seem to be contadictory on that. On the last line, if the bypass valve is opened completely, won't the danfoss thermostatically regulate itself? I thought it worked by sensing the water entering from the return side, and if it wasn't warm enough [say when below 140] it would introduce warming flow from the bypass. Then even if it worked the opposite (sensing bypass temp and [say when above 140] opening the return to introduce cooling flow from the return), I still don't see how manually valving down the bypass flow to it will put more flow through - that would seem to create a situation where you would be trying to direct more flow against what the danfoss would be trying to regulate through itself (making it fight itself?). Maybe I'm just overthinking things.
 
maple1 said:
Fred61 said:
maple1 said:
Isn't the Danfoss supposed to output the right temperature? I thought that was its function - not quite understanding why a manual valve would have to be added to make it work right.

The water flowing through the bypass line is what causes thr thermostat in the Danfoss to actuate. Circulator activates on return pipe and initially pumps water through the bypass line because at that point in time the automotive thermostat is closed. When the water flowing through the bypass line reaches 140 °F or whatever value you installed it flows on to the sensor part (bulb) of the thermostat and causes it to open. Colder water from your heating loop starts entering the boiler mixing with the warmer recirculating water.

Now you have two sources flowing, both tempering each other which more than likely will not allow the thermostat to open much or even possibly close again until the flow from the bypass warms the bulb. When the return water from the system reaches your desired temperature, in my case 140 °F the bulb will sense it and stay open, allowing circulation from the heating loop.

The variable restriction (ball Valve) placed in the bypass line is to limit the flow to your needs. Partially closing it restricts circulation through the loop, allowing more flow from the heat loop. I my case I hit the sweet spot on the ball valve about three years ago and haven't touched it since. Some of it has to do with my set points for circulator actuation but mostly has to do with my heat load or how much heat my flatplate exchanger can transfer into my unpressurized storage tank.

Wanna see how it works. Close the bypass valve completely and the Danfoss will never open.

I must be slow, I'm still not understanding it. Does the (hot) bypass loop actuate the thermostat, or the (colder) return line? The bolded above seem to be contadictory on that. On the last line, if the bypass valve is opened completely, won't the danfoss thermostatically regulate itself? I thought it worked by sensing the water entering from the return side, and if it wasn't warm enough [say when below 140] it would introduce warming flow from the bypass. Then even if it worked the opposite (sensing bypass temp and [say when above 140] opening the return to introduce cooling flow from the return), I still don't see how manually valving down the bypass flow to it will put more flow through - that would seem to create a situation where you would be trying to direct more flow against what the danfoss would be trying to regulate through itself (making it fight itself?). Maybe I'm just overthinking things.

I don't see that the two statements are contradictory. Perhaps if I said "The hot water flowing through the bypass line is what causes the thermostat in the Danfoss valve to actuate"
In the second bolded statement if I say " When the water from the heat distribution loop reaches your desired temperature, in my case 140 °F the bulb will sense it".

I don't know how to explain it any clearer. Perhaps if you don't think of it as being complicated and sleep on it you will understand. Or perhaps someone who explains things better than I can chime in.

PS. You do know what an automotive thermostat looks like, don't you?
 
Yes, and automotive thermostats don't need a manual valve added on to make them work - which is likely why I haven't got my head around this yet.
 