dmir

New Member
Jan 22, 2020
4
IL
I have a ~15 year old Heatilator GCDC60 and every winter it feels like I have a window open with the amount of cold air that flows into my house. Is this just the nature of the beast and not much can be done or could there be a damper or something stuck open? I dont think there are any dampers in the(sidewall) flur assembly based on my research but I cannot imagine this system was design to allow this much cold air in (and heat out) of my house. Is it maybe the contractor that built the house just didnt properly insulate the area around the fireplace? ANy input would be much appreciated. Thanks
 
Is this unit in a "Bumped out" (aka Dog House) type of construction?
Where do you feel the cold air? Bottom? Top?
 
See if you can remove that grate, or louver. With a flashlight,
look at the walls of the fireplace shell. Anywhere you see a hole thru
that shell, block it with unfaced fiberglass insulation or with aluminum tape.
That bump out is an unheated space, outside of the heated envelope of your home.
Your fireplace is steel & it gets cold. Any air IN that cold cavity will find its way into your home.
I assume you don't have an issue when the unit is burning...
 
See if you can remove that grate, or louver. With a flashlight,
look at the walls of the fireplace shell. Anywhere you see a hole thru
that shell, block it with unfaced fiberglass insulation or with aluminum tape.
That bump out is an unheated space, outside of the heated envelope of your home.
Your fireplace is steel & it gets cold. Any air IN that cold cavity will find its way into your home.
I assume you don't have an issue when the unit is burning...
Ok, thank you for taking the time to respond. I have already insulated some of the holes and my assumption has always been the bump out was just poor construction. I just wanted to be sure there wasn't a damper or another opening that could be stuck open or malfunctioning. Never an issue when heating. Thank you.
 
  • Like
Reactions: DAKSY