keyman512us said:
First off: "Welcome to all the 'newbie's..." here in this thread...
Secondly...I'm enjoying following this thread...very informative.
This is the "first mention" of HRV's I can think of here on the forum.
Tight houses are still more the exception that the rule, but they are becoming much more common given concerns about mold and the desire to save energy.
As houses become tighter (less air leakage) they provide less fresh air for occupants and it becomes necessary to introduce fresh air mechanically to the structure. HRV's do this while recovering a significant amount of the heat from the exhausted stale air. ERV's do the same thing but also recover moisture however they are limited to operation either in climates or during times of the years that there is no risk of freezing (one can swap an ERV core for and HRV during the winter for areas where there is freezing).
The problem is that very few builders, engineers or stove installers have ever worked extensively with tight homes and virtually none I have come across fully understand how to do a make up air audit let alone design a well thought out system. It's not that it is complex, but rather no one skilled in the art has every published an accurate point by point how to manual.
My own interest in the subject started when I was told it wasn't possible to have a traditional Rumford open hearth fireplace in a tight home. Two years and a fair amount of research later I came to the conclusion this was nonsense. It certainly wasn't possible if one failed to provide for adequate make up air (which seems to have been the source of this belief) but was quite straight forward if one did.
Having calculated the amount of air the house I was working on would require to keep depressurization below a level that would materially impact either the wood stove or the fireplace I then began to research various method to provide it.
Active make up air is the default practice in commercial buildings but I decided against them for reason of cost and long term reliability. It just wasn't clear to me someone would understand the necessity to have the fan in 20 years and if having eliminated it would fail to comprehend the reasons why the fireplace was smoking.
I therefore went with a passive system. Since I wanted whole house fan anyway for evening cooling on those days AC wasn't required I calculated what size opening would be enough to supply the air. 16 square feet was about the answer which was pretty close to the size of a standard whole house fan. That was convenient so I figured out a way that the same opening could be used to supply the make up air. If there is sufficient interest I'll describe it as it is a pretty cute design.
But as I continued to work on the HVAC system the idea of using the HRV came into focus. That was just too sweet to ignore so that is what I went with in the end. I still have the honking hole if for some reason the HRVs aren't able to supply the required flow, but I am fairly certain they will for all but the most extreme conditions.
Of course I won't know for sure until the sheet rock and all the window and doors are in at which time I will be able to do the blower door test. If the leakage is less than I project (which is good actually) and we go with a grill on the kitchen range (which requires gobs of air) then I might need to make use of the passive air when the kitchen hood is going full blast.
If nothing else what I have learned from this experience is to be wary of experts who can't adequately explain why what they say is true, because it often is a sign they are operating from long held beliefs that may or may not be supportable once examined carefully.
I also came to believe that extremely tight houses are a very, very good idea, as are unvented crawl spaces.
And finally that these types of structures work fine with an open hearth fireplace. You just have to plan carefully and know what you are doing.
Just don't forget the air tight chimney cap.