Eric Johnson said:
Speaking of hot water storage, I'm scrambling around trying to design a couple of heat exchangers for my 1,000-gallon tank. I have about 200 feet of rigid copper that I want to tear out and replace with pex-al-pex, and use the copper to make the hx. A conventional heat-loss calculation for 1" copper comes out to about 750 btu per foot per hour, meaning that it would take 200 feet to transfer 150K btu/hour into the tank. But I've been advised that I can probably get away with less, for a variety of reasons.
Heat transfer is flow (GPM) x delta (degrees F) x 500 So you could get 150k btuh by pumping 10 GPM and having a temperature drop (gain on the recovery coil) of 30 degrees. If you were only getting a 15 degree drop over the length of the coil, but could manage 20 GPM (not that you'd want to run 20GPM through 1" copper), you would get the same output. Similarly, if you could get a 60 degree drop, you could get by with only 5 GPM.
Which is to say that the larger the coil's surface area, the less flow you need, which means smaller pumps and less stress on them. Expensive as copper is, small coils are generally not a good idea.
Eric Johnson said:
If you were me, how much copper would you use for each one (heat recovery on the top and heat storage on the bottom) and how would you build it? I know the fittings add some surface area, but they are also potential leak sites. Would you put a lot of copper into smaller, more compact hxs or spread it out into longer runs? My tank measures roughly 4x6x7'
The length of the coils should be balanced, unless you have a lower heat demand (heat loss for structure) than heat gain (output of boiler). Since it sounds like you want to use what you have, I would suggest simply figuring the ratio of the heat demand to the boiler output, and dividing the copper that way.
Typically, an input coil works well in a nice compact arrangement at the center, as it will cause convection. The output coil should be large and openly-spaced, to gather heat from all over within the tank (don't want to create localized "cool" spots, as they won't convect as easily, and may linger near the coil). I wouldn't suggest a top and bottom arrangement, unless the tank is low and flat. I'm assuming from your dimensions that the 7-feet is the height. In that case, I would suggest concentric coils, with the input coil in the center and the output coil around it. Figure the diameter of the output coil to be 2/3 the tank diameter (assuming a round tank - obviously yours is not, but diameter is an easier way to describe it), and the inner coil to be about 1/3 the tank diameter. The stratification of the tank still comes into play, so you don't want place them evenly. The input coil should extend from the bottom to about 2/3 of the way up, and the output coild should extend from the top to 2/3 of the way down. You want to create flow, to keep things even, so you want to avoid adding heat to the top third of the tank, and removing it from the bottom third - the imbalance will create nice currents within the tank.
If you do a "spiral" sort of layout (relatively horizontal tubes, as opposed to relatively vertical tubes), plan on having the input coil flow down, and the output coil flow up. Since this will put the coolest part of the coil near the coolest water in the tank, heat transfer will be enhanced. I would probably type up some more, but I think dinner is ready...
Joe
Brownian Heating Technology