Building a chase

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

sly22guy

New Member
Hearth Supporter
Oct 28, 2008
42
Lancaster,PA
Building a chase for my englander 30 wood stove. the chimney is straight up and will be using the Duraplus 6" pipe. it says 2" clearance for combustables. so should i just make a wood frame and wrap with drywall or should i have something on the inside of the chase also (fire retardent material)? or just the 2" clearance?
 
All you need is a 2" AIR SPACE clearance around the pipe all the way up. You could make a cylindrical wood structure exactly 2" away all the way around and it would be safe according to UL testing.
 
You can even insulate the inside of the chase if you want to...so long as there's nothing combustible within 2" of the pipe anywhere in the chase. Rick
 
If you do put insulation inside the chase make sure it is secured so it could never slump and fall onto the side of the pipe.

Also the 2" clearance is not a "to combustibles" clearance, it is an AIR SPACE clearance. Which means the only thing allowed in that 2" space around the pipe is air. Only exception is UL approved firestops and roof flashings.
 
Yeah so i just need a 2" gap around on all sides. so the outside of the chimney is 10" in dia so i would need a 14" area. thanks
 
jtp10181 said:
If you do put insulation inside the chase make sure it is secured so it could never slump and fall onto the side of the pipe.

Also the 2" clearance is not a "to combustibles" clearance, it is an AIR SPACE clearance. Which means the only thing allowed in that 2" space around the pipe is air. Only exception is UL approved firestops and roof flashings.

hmm...

I just installed my chimney this weekend and I have it passing through a hole in the 1/16" aluminum soffit which is cut to size of the pipe. Is that a problem? After the soffit piece, it passes through the soffit and roof with a standard roof flashing.
 
No an alum soffit should be fine, that's basically the same thickness as a fire stop. If it was a 1ft thick concrete slab then the hole would have to be 2" bigger than the pipe.
 