Hi
I am curious how to calculate the number of times I would have to load and fire a wood boiler to supply primary heat and DHW to the house.
My house is 3500 square feet, heating by in-floor radiant heat connected to the DHW system which is currently heated via propane. I have calculated that I roughly use about 42,000 BTU/hour for DHW and house heat.
I think I can calculate how many hours the stove would need to burn to meet my heating needs. For example:
EKO 25
Rated at 85,000 BTU/hour
Rated at 91% efficiency = 77,350 BTU/hour
De-rate that efficiency by additional 25% to create a more real-world number
This comes to a real world figure of 56,100 BTU / hour.
I use about 1,000,000 BTU / day, so dividing 1M BTU / 56,100 BTU means I would need to run the stove for 18 hours to meet all of my needs.
Does that look right?
So 18 hours is an awful lot of burning, but I probably care less how long the stove will burn for and care more about how many times I have to go outside and fill it. This is where I am stuck. How do you figure this out?
By the way...is a 25% de-rate a reasonable number to use to approximate real world performance?
Thanks!
I am curious how to calculate the number of times I would have to load and fire a wood boiler to supply primary heat and DHW to the house.
My house is 3500 square feet, heating by in-floor radiant heat connected to the DHW system which is currently heated via propane. I have calculated that I roughly use about 42,000 BTU/hour for DHW and house heat.
I think I can calculate how many hours the stove would need to burn to meet my heating needs. For example:
EKO 25
Rated at 85,000 BTU/hour
Rated at 91% efficiency = 77,350 BTU/hour
De-rate that efficiency by additional 25% to create a more real-world number
This comes to a real world figure of 56,100 BTU / hour.
I use about 1,000,000 BTU / day, so dividing 1M BTU / 56,100 BTU means I would need to run the stove for 18 hours to meet all of my needs.
Does that look right?
So 18 hours is an awful lot of burning, but I probably care less how long the stove will burn for and care more about how many times I have to go outside and fill it. This is where I am stuck. How do you figure this out?
By the way...is a 25% de-rate a reasonable number to use to approximate real world performance?
Thanks!