I have a well that is 450' deep. Would it be possible to do geothermal heat with just that one well as well as continue to use it for potable water?
DickRussell said:Semipro's operation is called pump and dump. It saves needing enough water column to reheat the return water back to temperature by contact with the rock. That's why I said around 80 feet per ton is needed for the standing column well design where water is returned. With only 200 ft of water above the pump, that well can support perhaps 2.5 tons, or 30,000 BTU/hr sustained load. I'm guessing his heat pump is bigger than that, and that the house loses more than that on a cold winter night. He could get perhaps another ton of capacity out of that well by adding a 100 ft length of pipe to the suction side of the pump, capped at the bottom and perforated from say 20 to 40 feet up. That would force the return water down the extra distance below the pump, picking up extra heat from the rock, before entering the pump suction pipe. Still, 3.5 tons of capacity might be marginal, depending on the house.
There are various ways to address the pump issue when the well is used for both domestic water and circulation through the heat pump. One is to have a variable speed pump, which ramps speed up or down according to flow requirements. Another is to have the pump supply just enough pressure to circulate through heat pump and return to the well, with a booster pump on a side branch to provide higher pressure for the house plumbing. Of course there also is the need for a second pitless adapter for returning the water to the top of the well. Actually the return normally goes comfortably below the surface level in the well, which varies according to draw on the system at different times.
velvetfoot said:I have a well that is 450' deep. Would it be possible to do geothermal heat with just that one well as well as continue to use it for potable water?
Semipro said:DickRussell said:Semipro's operation is called pump and dump. It saves needing enough water column to reheat the return water back to temperature by contact with the rock. That's why I said around 80 feet per ton is needed for the standing column well design where water is returned. With only 200 ft of water above the pump, that well can support perhaps 2.5 tons, or 30,000 BTU/hr sustained load. I'm guessing his heat pump is bigger than that, and that the house loses more than that on a cold winter night. He could get perhaps another ton of capacity out of that well by adding a 100 ft length of pipe to the suction side of the pump, capped at the bottom and perforated from say 20 to 40 feet up. That would force the return water down the extra distance below the pump, picking up extra heat from the rock, before entering the pump suction pipe. Still, 3.5 tons of capacity might be marginal, depending on the house.
There are various ways to address the pump issue when the well is used for both domestic water and circulation through the heat pump. One is to have a variable speed pump, which ramps speed up or down according to flow requirements. Another is to have the pump supply just enough pressure to circulate through heat pump and return to the well, with a booster pump on a side branch to provide higher pressure for the house plumbing. Of course there also is the need for a second pitless adapter for returning the water to the top of the well. Actually the return normally goes comfortably below the surface level in the well, which varies according to draw on the system at different times.
That all sounds about right. We use this system to maintain a temp of about 62-65 in the house then use a wood stove and small space heaters when needed.
Our returning water to a sinkhole about 100 ft. away instead of to the well has the effect of extracting more heat from the aquifer.
I've never heard it called "pump and dump" but that makes sense. This site has pretty good descriptions of the systems including ours as a "standing column" system.
(broken link removed)
The HP system has been operating for about 25 years and for at least the last 12 years the same pump has supplied HP and drinking water at 60 PSI max. This is wasteful as the HP doesn't need that kind of pressure. I'm just now converting to a system where I'm adding a booster pump for domestic use at 70 PSI and adjusting the pressure sensor to shut the well pump off at a much lower pressure (about 30 PSI). I'm doing this to save energy and wear and tear on the well pump. For various reasons, this makes more sense than going with a variable speed well pump.
I do have concerns about well contamination and so forth with this type of system. If I ever have the need to trench around my place I might well consider converting to a closed loop system.
maple1 said:Semipro said:DickRussell said:Semipro's operation is called pump and dump. It saves needing enough water column to reheat the return water back to temperature by contact with the rock. That's why I said around 80 feet per ton is needed for the standing column well design where water is returned. With only 200 ft of water above the pump, that well can support perhaps 2.5 tons, or 30,000 BTU/hr sustained load. I'm guessing his heat pump is bigger than that, and that the house loses more than that on a cold winter night. He could get perhaps another ton of capacity out of that well by adding a 100 ft length of pipe to the suction side of the pump, capped at the bottom and perforated from say 20 to 40 feet up. That would force the return water down the extra distance below the pump, picking up extra heat from the rock, before entering the pump suction pipe. Still, 3.5 tons of capacity might be marginal, depending on the house.
There are various ways to address the pump issue when the well is used for both domestic water and circulation through the heat pump. One is to have a variable speed pump, which ramps speed up or down according to flow requirements. Another is to have the pump supply just enough pressure to circulate through heat pump and return to the well, with a booster pump on a side branch to provide higher pressure for the house plumbing. Of course there also is the need for a second pitless adapter for returning the water to the top of the well. Actually the return normally goes comfortably below the surface level in the well, which varies according to draw on the system at different times.
That all sounds about right. We use this system to maintain a temp of about 62-65 in the house then use a wood stove and small space heaters when needed.
Our returning water to a sinkhole about 100 ft. away instead of to the well has the effect of extracting more heat from the aquifer.
I've never heard it called "pump and dump" but that makes sense. This site has pretty good descriptions of the systems including ours as a "standing column" system.
(broken link removed)
The HP system has been operating for about 25 years and for at least the last 12 years the same pump has supplied HP and drinking water at 60 PSI max. This is wasteful as the HP doesn't need that kind of pressure. I'm just now converting to a system where I'm adding a booster pump for domestic use at 70 PSI and adjusting the pressure sensor to shut the well pump off at a much lower pressure (about 30 PSI). I'm doing this to save energy and wear and tear on the well pump. For various reasons, this makes more sense than going with a variable speed well pump.
I do have concerns about well contamination and so forth with this type of system. If I ever have the need to trench around my place I might well consider converting to a closed loop system.
Why not just turn your pressure down? Our domestic water pump cuts in at 20psi & shuts off at 35psi. I can't imagine needing 60 or 70psi.
maple1 said:I've got filters too. A parallel pair of 5 micron sediment ones, in series to a parallel pair of charcoal ones. The only time the upstairs shower gets bad pressures is when the filters need changing (the charcoal ones seem to plug first). Might come down to what your use to though. We don't have 'water saving' shower heads. I could definitely see a drop when the HP comes on. How much does it flow? My buddy put in a ground loop 5 ton HP this summer, I'm waiting to see how much his electric bill ups when the winter's over. Very interesting but don't really want to tear up the yard & beyond like he did.