Central Boiler is now claiming 85% efficiency for their e-classic boilers.
(And implying this is overall since, they claim the combustion efficiencies are almost 100%).
At the same they indicate that when the stove is burning at 150,000 Btu's output the stove will burn for 8 hours.
All of this from their website.
http://www.centralboiler.com/e-classic.html
Note that the overall efficiency values also appear on the EPA website.
So here are my computations.
Firebox = 27 cu ft or .21 cords.
1 cord of hardwood = 22 million btu's.
.21 x 22 million = 4.62 million btu's potential when fully loaded.
8x150,000=1.2 million btu's.
1.2/4.62 =
Overall efficiency = 26%.
Is my math is wrong here?
If not where does the difference come from.
Does central boiler recommend loading the boiler significantly less than full.
If so what is their recommendation.
Also has anybody ever tried burning the eclassic 2300 with a completely full firebox.
If so what were the problems if any.
If not what's the size of the average load during the coldest weather.
(And implying this is overall since, they claim the combustion efficiencies are almost 100%).
At the same they indicate that when the stove is burning at 150,000 Btu's output the stove will burn for 8 hours.
All of this from their website.
http://www.centralboiler.com/e-classic.html
Note that the overall efficiency values also appear on the EPA website.
So here are my computations.
Firebox = 27 cu ft or .21 cords.
1 cord of hardwood = 22 million btu's.
.21 x 22 million = 4.62 million btu's potential when fully loaded.
8x150,000=1.2 million btu's.
1.2/4.62 =
Overall efficiency = 26%.
Is my math is wrong here?
If not where does the difference come from.
Does central boiler recommend loading the boiler significantly less than full.
If so what is their recommendation.
Also has anybody ever tried burning the eclassic 2300 with a completely full firebox.
If so what were the problems if any.
If not what's the size of the average load during the coldest weather.