hammmitc said:
I have a two story home with a brick exterior chimney with a standard (terra cota?) liner. The liner is in good shape, kept it clean, no creosote buildup at all. Chimney is about 25ft high and has an excellent draft. The house is about 20 years old, the fireplace was used maybe 4 times a year over that time period. Can I get away with not using a SS liner until the chimney needs it? I will use some flex liner to get past where the flue is located and plan on using a block off plate.
I am looking at a Napolean 1201P or a Regency I3100 for a 2700 sq ft home.
There are three issues - chimney condition, flue size, and climate
1. Chimney condition - If a flue is not up to NFPA standards, it must be lined, normally with an insulated liner to bring it up to code. - this doesn't sound like a problem for you.
2. Flue size - VERY likely a problem - current code says that an external chimney flue may not have a cross section area more than twice the area of the stove flue outlet. I don't memorize stove specs, but I think the two you mention use 6" flues, as do all but the largest of modern stoves. This means about 28 sq" - any clay liner larger than a nominal 8"x 8" will not be w/in that 2x 28" limit, and therefore you must install a full length liner to reduce the size to an appropriate number. Code does not "require" liners installed to meet cross section requirements in otherwise sound chimneys to be insulated, though it's a good practice.
3. Climate - An external chimney tends to have a problem with creosote buildup during stove operation, and with draft reversals any time you try to get it started. It can also have problems with poor drafting in general, draft works on heat differential, and an external chimney can cool a stoves exhaust enough to cause it to draft poorly, especially when it is cooling off towards the end of a burn. Many refer to them as "Evil Chimneys". The colder the climate, the more problems, and most of PA is cold enough to be considered a problem. Insulating the liner is not cheap, but it doesn't add that much to the job as part of the overall cost of a stove installation, and can result in major improvements in stove performance. General concensus is that if you can insulate (you may not have room, though there are things that will help even then) you should.
There are a couple side benefits to the liner however,
1. You will find that it makes chimney cleaning FAR easier if you do it yourself, and usually cheaper if you have it done.
2. In the unlikely event of a chimney filre, the liner will significantly increase your odds of riding it out without any damage - this is greatest with an insulated liner, but any liner will help contain the fire.
Gooserider