Hey folks,
Have been playing with the pump size tool at (broken link removed to http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf)
Everything seems straight forward until we get to head loss.
I dont know the pipe length for my 3rd zone as yet, but in my first two zones I used 500ft of AL-PEX total for all pipework, the calculator says I need a flow rate of 14 GPM.
HL = k * c * L * (f ^1.75)
0.0034 * 0.933 * 500 * ( 14 ^1.75 )
=161 ft head
This seems to be off the charts.
Am I including too much pipe?