This is a sticky inspired by Tenman, who suggested it as a topic to address one of the most critical components in a boiler system, namely the underground line set for those installations where the boiler and / or storage is in a different building from where the heat load is.
Not all installs use underground lines, and it is this moderators opinion that if it is practical, one is better off designing a system to avoid them, however this is often not possible.
However, it is worth noting that if an underground lineset is used, it will probably be one of the most expensive parts of the entire installation, sometimes costing even more than the boiler itself. It certainly is the most difficult and expensive part to have to redo if one doesn't get it "right" the first time around.
It can also be a critical part to determining the performance of an entire system, with bad design choices causing poor system performance, high operating costs, and excessive wood consumption....
If one goes through the threads here in the boiler room, I would say that after the standard causes for performance issues such as bad weather sealing, and less than ideally seasoned wood, bad line set design is one of our more common issues, and one of the harder issues to fix.
This is NOT the place to try and save money by going cheap on the design!
So how does one do it right?
1. Make it big enough - there is an often linked to Taco paper on sizing pumps and other system components, including the lines. (broken link removed to http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf) Before doing any other planning, figure out the heat loads, and determine the size of the piping needed, per the formulas in this paper. In case of doubt, go bigger.
Lines that are to small will cause problems of not delivering enough heat on cold days, or doing so only by using excessively large and power-hungry pumps (which can have their own problems, particularly on open systems)
OTOH, there are relatively few problems caused by oversized lines.
Note that large sizes of PEX can be hard to find, and even worse to get fittings for, not to mention the high costs of the tooling needed for the very few connections one will need to make - it can sometimes be advantageous to do multiple parallel runs of a smaller size PEX, something that works especially well if using the "Foam in Place" insulation method described below.
2. KEEP IT DRY - one of the common failure modes for lines is to have ground water infiltrate the insulation system. A system that may work perfectly when dry can become nearly worthless if it becomes compromised by moisture, as damp insulation becomes a good thermal conductor, and once wet drying an underground line is nearly impossible. Pay attention to drainage in the trenches, with plenty of gravel and so forth to keep the water away from the lines. Even more important, choose insulation materials that are in themselves waterproof - we see lots of horror stories about lines that are wrapped in bubble wrap and stuffed into a drain pipe, especially after they have been in service for a few years. OTOH, there are several very successful installs with closed cell spray in place foam installed in a properly prepared trench.
3. Keep the runs short - saves money, and the less time underground, the lower the temperature drop that even the best lines will experience....
4. Insulate it adequately - Even a one or two degree no-load temperature drop going through the lineset can add up to a suprisingly large amount of heat loss over the course of a heating season, possibly as much as several added cords of wood worth....
5. Include some "support" lines - I always urge that unless you have already included other provisions for it, that you include a few runs of 3/4"conduit for electrical power and / or computer data lines (remember you can't put low voltage stuff like data lines, and AC power in the same conduit) Those extra runs cost almost nothing to add when the trench is open, but can be a problem to add later...
Gooserider
Not all installs use underground lines, and it is this moderators opinion that if it is practical, one is better off designing a system to avoid them, however this is often not possible.
However, it is worth noting that if an underground lineset is used, it will probably be one of the most expensive parts of the entire installation, sometimes costing even more than the boiler itself. It certainly is the most difficult and expensive part to have to redo if one doesn't get it "right" the first time around.
It can also be a critical part to determining the performance of an entire system, with bad design choices causing poor system performance, high operating costs, and excessive wood consumption....
If one goes through the threads here in the boiler room, I would say that after the standard causes for performance issues such as bad weather sealing, and less than ideally seasoned wood, bad line set design is one of our more common issues, and one of the harder issues to fix.
This is NOT the place to try and save money by going cheap on the design!
So how does one do it right?
1. Make it big enough - there is an often linked to Taco paper on sizing pumps and other system components, including the lines. (broken link removed to http://www.taco-hvac.com/uploads/FileLibrary/SelectingCirculators.pdf) Before doing any other planning, figure out the heat loads, and determine the size of the piping needed, per the formulas in this paper. In case of doubt, go bigger.
Lines that are to small will cause problems of not delivering enough heat on cold days, or doing so only by using excessively large and power-hungry pumps (which can have their own problems, particularly on open systems)
OTOH, there are relatively few problems caused by oversized lines.
Note that large sizes of PEX can be hard to find, and even worse to get fittings for, not to mention the high costs of the tooling needed for the very few connections one will need to make - it can sometimes be advantageous to do multiple parallel runs of a smaller size PEX, something that works especially well if using the "Foam in Place" insulation method described below.
2. KEEP IT DRY - one of the common failure modes for lines is to have ground water infiltrate the insulation system. A system that may work perfectly when dry can become nearly worthless if it becomes compromised by moisture, as damp insulation becomes a good thermal conductor, and once wet drying an underground line is nearly impossible. Pay attention to drainage in the trenches, with plenty of gravel and so forth to keep the water away from the lines. Even more important, choose insulation materials that are in themselves waterproof - we see lots of horror stories about lines that are wrapped in bubble wrap and stuffed into a drain pipe, especially after they have been in service for a few years. OTOH, there are several very successful installs with closed cell spray in place foam installed in a properly prepared trench.
3. Keep the runs short - saves money, and the less time underground, the lower the temperature drop that even the best lines will experience....
4. Insulate it adequately - Even a one or two degree no-load temperature drop going through the lineset can add up to a suprisingly large amount of heat loss over the course of a heating season, possibly as much as several added cords of wood worth....
5. Include some "support" lines - I always urge that unless you have already included other provisions for it, that you include a few runs of 3/4"conduit for electrical power and / or computer data lines (remember you can't put low voltage stuff like data lines, and AC power in the same conduit) Those extra runs cost almost nothing to add when the trench is open, but can be a problem to add later...
Gooserider