Hi Leon, thanks for the input . . . Wood is a waste product for me . . . so I am using it as free fuel . . .
Let me make sure I understand: you say the circulators should be on the SUPPLY side, pumping HOT water to the zone? I was under the assumption that they PULLED water from the zone and were placed on the RETURN side feeding into the boiler?
Thanks for the info on the expansion tanks, I'll look at that and make the change . . .
==========================================================================================
Yes, that is how I have my single circulator and It works perfectly fine and it helps to pull any remaining micro air bubbles out and into the steel expansion tank as there is no need for the air scoop.
You can plumb the circulator any way Doug, but the ideal way is to install them on the top of the boiler with isolation flanges preferably with the isolation flanges with drain cocks so you can drain the water in the impeller chamber into a bucket before you unbolt the circulator from the flanges.
I have a vacuum gauge on the suction side of the circulator and a pressure gauge on the discharge side of the circulator and that lets me know if the circulator is going bad because it will be pulling a large vacuum pressure gradient "Hg". I also have a pressure and temperature gauge on the return line to the sump of the coal stoker to keep track of water temperatures.
I also have a 4 inch square bottom tapping Marsh instruments Marshalltown pressure and altitude gauge in the steam chest
of my coal stoker because Keystoker has been using junk Chinese Gauges and digital boiler controls and I almost had my house get blown up because the Hydrolevel 3250 Plus did not shut my boiler down when it had a low water condition.
The use of a true triple gauge lets you set your operating pressure with a manually adjusted pointer on the dial and you can always see how the boiler(s) is/are working and you can operate at a very low pressure at all times- mine runs between 4-12 pounds at all times and you can run at very low operating temperatures too. I have run my system at 140 low 160 since I installed the old hand fed wood and coal boiler and it works fine it only does not heat well when I use oil as I have no additional storage but I do not burn that much oil anyway so....
I got rid of all that digital junk and installed a Honeywell L8124L1011 triple aquastat and a B+G Bulldog RB-122-E low water cut off after the replacement Hydrolevel 3250 Plus turned the Low Water cut off function off while I ran the boiler on oil to test it.
The Hand fed wood and coal boiler I had which was tied into the oil boiler for back up had 2 simple strap on honeywell aquastats and a Honeywell L8214 triple aquastat to control the oil boiler if the wood and coal hand fed boiler got too cold if the fire went out and I never had an issue using that set up for 33 years.
==========================================================================================
As I said plumbing the boilers in series saves money and work and if you want to use oil just shut off the wood boiler and let the all water flow through the oil boiler unhindered without installing boiler to boiler bypass plumbing. Just be sure isolate the boilers with 4 good ball valves and 4 unions to allow for any forseable repairs or an oil boiler change outs
==========================================================================================
The boiler builders installed circulators on the bottom pumping to the boiler that way years ago to simply save crating cost when they shipped the packaged boilers they designed for one story homes using hot water heat.
The plumber or homeowner had to drain the boilers to change circulators which becomes messy at times and can cause electrical problems too if you have a leak as well as cause accidental electrocutions.
I will suggest very very strongly that you order two paper back books "Pumping Away" and "Classic Hydronics" written by Dan Holohan. Dan is a former plumbers helper, plumber and HVAC technical sales rep that has been in the business for many years and when he writes about plumbing and heating he makes it fun to read and easy to understand for both the layperson/homeowner and plumber.
Pumping Away is a small paperback with large type and Classic Hydronics is a wire bound book which make it easy to
rear and show the many plumbing designs that have been invented and it has larger type as well.
You can purchase his paperback books directly from him at (broken link removed) and eliminate the middleman.
I have both of these paperback books as well as "What Hydronics Taught Dan Holohan" and they are well written and easy to understand and he goes into detail talking about plumbing and heating and the history of plumbing and heating and he makes it fun to read and he brings real world examples to show the reader about plumbing history of all types and as I said you will have fun reading these books.