I have a 20 year old Majestic DV360 natural gas fireplace. In place of an on/off wall switch I use a furnace thermostat.
Over time it seems that once the pilot is lit and the Honeywell gas valve is turned to the on position, it's been taking longer and longer (on the order of several minutes now) for the burner to ignite once the thermostat is turned to heat with the set point above the room temperature. I can hear the thermostat click as the contacts close.
I did some testing of the thermopile output once the gas valve was in the on position and it appears that it is slow in getting to the 325mV output necessary to operate. Does this indicate the thermopile is on the way out or that it might just need cleaning?
In working on this problem I saw a couple flame-related things that I would like some opinions on. One is with the pilot and the other with the burner flame.
With the pilot I'm concerned about the flame that can be seen in that narrow slit next to the thermopile. It looks like it is underneath the "platform" that the thermopile, thermocouple, etc. sit on. Is that OK or is there gas leaking where it shouldn't be?
With burner I expected the flame to kind of uniform be all across the width whereas it appears to be just in certain dintinct spots. Is this pattern normal?
Thanks for any input!
Over time it seems that once the pilot is lit and the Honeywell gas valve is turned to the on position, it's been taking longer and longer (on the order of several minutes now) for the burner to ignite once the thermostat is turned to heat with the set point above the room temperature. I can hear the thermostat click as the contacts close.
I did some testing of the thermopile output once the gas valve was in the on position and it appears that it is slow in getting to the 325mV output necessary to operate. Does this indicate the thermopile is on the way out or that it might just need cleaning?
In working on this problem I saw a couple flame-related things that I would like some opinions on. One is with the pilot and the other with the burner flame.
With the pilot I'm concerned about the flame that can be seen in that narrow slit next to the thermopile. It looks like it is underneath the "platform" that the thermopile, thermocouple, etc. sit on. Is that OK or is there gas leaking where it shouldn't be?
With burner I expected the flame to kind of uniform be all across the width whereas it appears to be just in certain dintinct spots. Is this pattern normal?
Thanks for any input!