Hi Folks,
How's that for a searchable title?
I've been researching exterior chase construction, and thought I'd pass on what I've learned.
I'm planning to optimize the draw of my exterior chimney by enclosing it, and bringing the chase below the roofline into the building's heated envelope, and insulation the portion above the roof.
The toughest question was whether to vent the portion above the roofline. From what I've seen, the standard practice is to leave the upper chase both unsealed and uninsulated, with a vent at the top to release whatever moisture enters from the loose construction. For example, here's Simpson's DuraTech chase-top flashing, which has a 13" hole for a 10" OD 8" ID Class A chimney pipe:
(broken link removed to http://www.northlineexpress.com/item/5SP-9630/8-Simpson-DuraTech-Chase-Top-Flashing-9630)
I wanted to do better, insulating the upper chase to hold heat and improve draw, to keep that big 8" wide flue from stalling with a cat stove's sometimes slow and cool flue gases. As I said above, venting is SOP, but is it necessary? Is it legal and advisable to seal a tight, sealed, and insulated chase, or might there be problems?
My research says that sealing is beneficial and legal. I'll include the evidence below, and a link to it's source, in case it's useful. Please feel free to make any comments or corrections.
It also has some interesting discussion of metal versus masonry flues, and chimney fires, which I included for general interest. I'll have to break it into parts, because of the character limit. :/
Best,
George
From The Journal of Light Construction:
http://forums.jlconline.com/forums/showthread.php?t=47395
How's that for a searchable title?
I've been researching exterior chase construction, and thought I'd pass on what I've learned.
I'm planning to optimize the draw of my exterior chimney by enclosing it, and bringing the chase below the roofline into the building's heated envelope, and insulation the portion above the roof.
The toughest question was whether to vent the portion above the roofline. From what I've seen, the standard practice is to leave the upper chase both unsealed and uninsulated, with a vent at the top to release whatever moisture enters from the loose construction. For example, here's Simpson's DuraTech chase-top flashing, which has a 13" hole for a 10" OD 8" ID Class A chimney pipe:
(broken link removed to http://www.northlineexpress.com/item/5SP-9630/8-Simpson-DuraTech-Chase-Top-Flashing-9630)
I wanted to do better, insulating the upper chase to hold heat and improve draw, to keep that big 8" wide flue from stalling with a cat stove's sometimes slow and cool flue gases. As I said above, venting is SOP, but is it necessary? Is it legal and advisable to seal a tight, sealed, and insulated chase, or might there be problems?
My research says that sealing is beneficial and legal. I'll include the evidence below, and a link to it's source, in case it's useful. Please feel free to make any comments or corrections.
It also has some interesting discussion of metal versus masonry flues, and chimney fires, which I included for general interest. I'll have to break it into parts, because of the character limit. :/
Best,
George
From The Journal of Light Construction:
http://forums.jlconline.com/forums/showthread.php?t=47395
Old 04-10-2009, 11:51 AM
tucker tucker is offline
Veteran Contributor
Join Date: Aug 2004
Location: West Virginia, Cold Climate w/ wind
Posts: 220
Default Re: Insulated Chimney Chase?
Sorry about the lack of info. It is a wood burning/optional gas log unit, a lennox superior fireplace to be exact, with double walled chimney . The clearances from combustibles are 1" to unit and 2" to chimney sections(I usually triple that atleast). The chimney section has no offsets, it is straight and about 13' tall with 8' of that above the roof plane. I am not asking about specific installation instructions like clearances, but more about the pro's and cons of insullating the above roof chase.... Chimeny draw vs condensation problems.
I have used this model a couple times and have always followed the manufacturers directions for chase construction, but instructrions have said insulation is recommended but optional in chase walls(installation guidelines also say do not use blown or fill type insulation). I have always insulated with unfaced fiberglass then used 1/4 hardiebacker for interior(although manufacturer recommends osb, plywood, or drywall).
I am just wondering about condesation issues since the chase cap is uninsulated and would be a cold surface, but I am also wondering about condesation in chase wall system....but now that I think about it wouldn't most of the warm air generated by the chimney section be fairly dry?
As for AHJ, I am in a no inspection area...& a six pack will get you a building permit ; )
#4
Old 04-11-2009, 09:06 PM
Hearthman Hearthman is offline
Veteran Contributor
Join Date: Oct 2007
Location: Northeast
Posts: 119
Default Re: Insulated Chimney Chase?
You are describing a factory built fireplace listed to UL 127 for woodburning. These fireplaces are usually tested to also use optional vented gas logs listed to ANSIZ21.60 and in some cases, ventfree logs listed to ANSI Z21.11.2b . There is no such thing as "direct vent" with wood burning. Direct vent means self contained combustion/ makeup air and exhaust.
The listing does not require any type of fire resistive construction in the chase. However, if you do insulate the chase, you must protect the insulation from falling in contact with the fireplace and chimney. The building code dictates this construction. Basically, you want to bring the fireplace inside the thermal envelope of the home. This means foam, caulk, air sealing, insulation, a low flame spread sheathing and reducing air infiltration. Having said that, you cannot caulk listed firestops unless specifically allowed by the mfr.s listed instructions.
You must provide proper fireblocking around listed firestops per your local codes. In the absence of any locally adopted codes, you should still build to the IRC, which is now the default building code referenced in the US. Therefore, fireblocking would then comply with IRC 602.8 .
Once you get above the attic deck, there is no requirement by the codes to weatherize the chase walls since you are outside the thermal envelope. Doing so would provide some improvement in draft and minimize flue gas condensation. However, it would have little if any effect on condensation inside the chase. I enter these chases all the time and the only moisture problems I find are from leaks and faulty installation.
There is no need to triple the stated clearances off the chimney. In fact, you cannot at the firestops since they should be braced and supported laterally. The listing allows a max. chase temp. rise of 90*F above ambient so don't lose sleep over it. Properly installed, these fireplaces are much safer than masonry fireplaces and unlike masonry, come with a warranty and are listed. BTW, a masonry fireplace was tested to UL 127 back in 1984 and the test structure ignited!
Tucker, I don't think you will see any significant condensation issues in a properly constructed chase built to code and the fireplace installed to the listed instructions.
HTH,
Hearthman