Well I'm excited that now going into our 6th season we finally have storage! I'm looking forward to experiencing the benefits you guys talk about. The system is a BioMass 60, two 500 gal vertical tanks, and a Laddomat 21-100. Here's my first batch of storage newbie questions:
1 - I thought there was something wrong with my boiler last nite. After burning for an hour the boiler temp was barely increasing. Boiler temp was at 120F for a long time. Way below the 157*F Laddomat turn-on temp set in the RK2001. Flue temp was at ~220--230*F. So I presumed boiler output was choked somewhere, maybe the new nozzle protector. After about an hour I touched the pipes in and out of the Laddo. The pipe going to storage was warm, about 120*F (as shown on by the RK). Got a ladder and touched the storage manifold at the top of the tanks, warm. The water in storage was about 50*F at the start of the burn. So this must be the thermosyphoning I've read about but until now never concerned me. I closed the cold return valve into the Laddo and almost immediately started to see boiler temps rise. Is this normal? I was surprised that the Laddo allowed apparently a pretty sizeable thermosyphoning flow, enough that the BioMass couldn't get a good head of steam with 50*F water being pumped in.
2 - I opened the Laddo cold inlet valve right before the boiler hit the pump-on temp (157*F). With the Laddo on it seemed to manage circulation and the boiler climbed up into the 180's. Normal? This may be a first fire of the season issue. Obviously we'll be keeping storage between about 130*F - 180*F during the heating season.
3 - This morning the FUEL light was on probably due to bridging. I'd guess the boiler ran for ~5-6 hrs before that shutdown. Top tank temp is ~ 130*F, bottom ~ 70*F. What's the equation for how many hours it takes at some assumed output to get 1000 gal of 50*F water up to uniform temp. From last nite's experience that looks like it could be a long time. Good news to me is clearly there's energy going into the tanks, but to get the whole tank up to 180*F from 50*F could take a long time.
4 - I'm not circulating any flow to the house, so for the first time I have a pretty good means of calculating the boiler's output since all the energy is going to storage right now. I'd like to calculate real boiler output based on the time to get to a uniform stored energy in the 1000 gal.
5 - Is thermosyphoning is a good/normal thing between the boiler and storage with a loading unit? I'm sure once I get and keep storage in the 130-180*F range the thermosyphoning flow will be reduced. Since there's a pump to make this happen, you'd think boiler/storage thermosyphoning would be a good thing.
Thanks guys.
1 - I thought there was something wrong with my boiler last nite. After burning for an hour the boiler temp was barely increasing. Boiler temp was at 120F for a long time. Way below the 157*F Laddomat turn-on temp set in the RK2001. Flue temp was at ~220--230*F. So I presumed boiler output was choked somewhere, maybe the new nozzle protector. After about an hour I touched the pipes in and out of the Laddo. The pipe going to storage was warm, about 120*F (as shown on by the RK). Got a ladder and touched the storage manifold at the top of the tanks, warm. The water in storage was about 50*F at the start of the burn. So this must be the thermosyphoning I've read about but until now never concerned me. I closed the cold return valve into the Laddo and almost immediately started to see boiler temps rise. Is this normal? I was surprised that the Laddo allowed apparently a pretty sizeable thermosyphoning flow, enough that the BioMass couldn't get a good head of steam with 50*F water being pumped in.
2 - I opened the Laddo cold inlet valve right before the boiler hit the pump-on temp (157*F). With the Laddo on it seemed to manage circulation and the boiler climbed up into the 180's. Normal? This may be a first fire of the season issue. Obviously we'll be keeping storage between about 130*F - 180*F during the heating season.
3 - This morning the FUEL light was on probably due to bridging. I'd guess the boiler ran for ~5-6 hrs before that shutdown. Top tank temp is ~ 130*F, bottom ~ 70*F. What's the equation for how many hours it takes at some assumed output to get 1000 gal of 50*F water up to uniform temp. From last nite's experience that looks like it could be a long time. Good news to me is clearly there's energy going into the tanks, but to get the whole tank up to 180*F from 50*F could take a long time.
4 - I'm not circulating any flow to the house, so for the first time I have a pretty good means of calculating the boiler's output since all the energy is going to storage right now. I'd like to calculate real boiler output based on the time to get to a uniform stored energy in the 1000 gal.
5 - Is thermosyphoning is a good/normal thing between the boiler and storage with a loading unit? I'm sure once I get and keep storage in the 130-180*F range the thermosyphoning flow will be reduced. Since there's a pump to make this happen, you'd think boiler/storage thermosyphoning would be a good thing.
Thanks guys.