rvtgr8 said:
Jim,
You are right on so many levels. The corrected drawing (which also may be flawed) is included in this post. The boiler side has my Taco 007-5f. The thing that I did not include in my rushed drawing was the fact that there is a HX at the tub. No fluids will co-mingle with my Garn. Unless there is a significant heat loss associated with the constant sharing between the two systems I am okay with it. My logic may be flawed here though. If the propane boiler is always on and the Garn is not, it seems to me it would burn all the time because it would be losing heat back to the Garn through the HX. But my intention is to use the Garn nearly 100% of the time. Am I way off base?
I understand you redid some of your system...was it anything to do with this same situation? Is my drawing any clearer?
The Garn side looks OK, I don't see any real issues with the hot tub being on the Garn side as long as you don't mind the tub getting cold if the Garn does... If the tub was in series with the house HX, I'd be worried about it possibly stealing to much heat from the house, but since it's a seperate loop with it's own pump, no problem as the controls can be set to give the house priority as appropriate.
Where I still see a problem even with the pump relocated, is on the house side of the HX. You don't have anything keeping the Garn heat from going through the boiler, which I assume you don't want, and even more impotantly, you don't have anything that would make the water flow through the house side of the HX - there are two closely spaced tees, on the HX loop, with no pump to make water flow through them.
I see two possible options that might fix this...
1. Put a pipe across the radiant load so that you are making a pure load house radiant loop, and leave the existing pump on the load loop. Tie the Burnham to the load loop with a pair of closely spaced tees like the HX is, and put a small pump with a flow check on each of the resulting heat source loops. If the Garn is hot the HX pump feeds the radiant loop, and the boiler pump is off with no flow through its loop. If the Garn is cold the reverse applies.
2. Put one line of the HX house side on the other side of the Burnham so that the two sources are in parallel, and leave the house pump where it is. Put a ZV or motorized ball valve in each of the boiler and HX lines, (given your planned use, I'd make the boiler valve be NC and the HX valve be NO, just to save using the energy on actuating the valves most of the time). Set up your controls to open the valve on which ever unit is supplying the heat, and close the one on the other and let the house pump push the heat through the load and the source. EDIT - clarification - the house pump must be on the radiant load side of the circuit, not on either of the heat source parts, so in the drawing the house side of the HX would have to connect between the Burnham and the pump, not between the pump and the loads.
Either way, the idea is that you have isolated the source that isn't hot, and have circulation to the one that is...
Gooserider