I have a troy built 5500w gen. I'm going to wire the house this weekend and would like to know what size wire would be best. 8-3 or 10-3 thanks
Former Farmer said:10-3 romex is rated for 30 amps. 8-3 romex is rated for 40 amps. 5500 watts / 240 volts = 23 amps. You can get by with 10-3 wire. If the length of wire is going to be over 75 feet, use 8-3 wire for voltage drop.
What type of wire are you referring to? Romex, SO cord?
Remember to have a means of disconnecting from the local electrical provider so the power does not back feed onto the power grid.
seige101 said:Also do not forget the constant use de-rating factor, 80%. Making that #10 line good for 24 amps.
livefreeordie said:I should get more than P if i don't run a bunch of stuff all at once right? This is all new to me. All i want to do is run the fridge,some lights if i need them, the furance blower fan if needed and the pellet stove, maybe a TV. So i'm looking at one 30amp breaker and four 15 amp breakers thats it.
btuser said:livefreeordie said:I should get more than P if i don't run a bunch of stuff all at once right? This is all new to me. All i want to do is run the fridge,some lights if i need them, the furance blower fan if needed and the pellet stove, maybe a TV. So i'm looking at one 30amp breaker and four 15 amp breakers thats it.
If you don't have the well pump then you're all set. A simple transfer switch like Reliance with 6 breakers/switches will work. You're going to want the bathroom lights, some outlets, the fridge and the furnace. If you've got sub panels to run it gets more complicated. 30 amps (aka 10/3 ) is good enough.
velvetfoot said:You may be interested in putting in an interlock kit so that you can run anything, not pay that much, and still be safe. I have a SquareD panel so I got this one:
http://static.schneider-electric.us/docs/Electrical Distribution/Load Centers/Accessories-Homeline-HOM-LK-PK-QOM/40273-809-02.pdf
I would've used a 5kw generator I already had if it wouldn't have been for that darn deep well pump.
I do not understand that as I can run 30 amps through #10 wire for 24/7 and the wire will not even be warm to the touch as long as the voltage drop is with in the guide lines.wingman1776 said:If you are going to run a load on the line for long peroids on time you should de-rate the line by 20 % due to heat in the line. It is a standard code thing for saftey. 30 amps - 20 % = 24 amps
oldspark said:I do not understand that as I can run 30 amps through #10 wire for 24/7 and the wire will not even be warm to the touch as long as the voltage drop is with in the guide lines.wingman1776 said:If you are going to run a load on the line for long peroids on time you should de-rate the line by 20 % due to heat in the line. It is a standard code thing for saftey. 30 amps - 20 % = 24 amps
thinkxingu said:Yeah, it's cool--in my situation, I'll need to shut off all my electric heat circuits, but it will be nice to have the garage openers available and all the lights around the house. Thought we might need it this last storm, but nope!