Last heating season my Quad Castile would more often than not shut down before it completed its startup cycle. I could get it to go most times by setting the stove on high then lowering it to medium once it started and it will run fine thereafter. My gaskets are all good, exhaust pipe clean etc.
Today I tested the thermocouple with a multimeter and a portable propane torch. According to my service manual to go green (on the control box)) the system needs to see ~2.5mV, and to go the final Red ~12mV. The best I could get was ~4 mV. So I'm biting the bullet and ordering an OEM thermocouple. I'm begrudgingly doing so because I'm sure Quad is going to ask a hefty price, but I'm tired of coming downstairs in the AM and the stove cold.
We like coming down stairs on a cold winter morning and seeing the stove running. We really miss that! I wondered if a thermocouple output might diminish with long term use (mine is approximately 15 years old), but could never find any posts regardless of how much I searched.
Today I tested the thermocouple with a multimeter and a portable propane torch. According to my service manual to go green (on the control box)) the system needs to see ~2.5mV, and to go the final Red ~12mV. The best I could get was ~4 mV. So I'm biting the bullet and ordering an OEM thermocouple. I'm begrudgingly doing so because I'm sure Quad is going to ask a hefty price, but I'm tired of coming downstairs in the AM and the stove cold.