Bought Greenwood 100 in August from local agent and hired installer. Installation is indoors, linked to oil-fired boiler, for hot-water baseboard heating house of about 4000 sq ft. First-time experience with a wood boiler.
Installation proved lengthy, at about 70% of the price of the boiler. Duration of installation was due inter alia to the flow valve provided by GW not being the same as the one specified in the installation guide. Other issues involved the electrical interface with the oil-fired boiler.
After two or three successful trial runs lasting a day or two, a longer run was begun. It ended abruptly on the fifth day when the 1” pex hot water output tubing burst, which then produced overheating because hot water was not reaching the heat dissipation fan circuit. The output pipe was copper for the first 4 feet, then 1" pex, and the burst was 3 feet from the start of the pex (i.e. about 7 ft from the boiler). Simple repair, replacing pex with copper pipe. In hindsight, the aquastat controlling the fan operation may have been set too high; a lower setting might have eased the heat/pressure buildup and precluded the pipe burst.
My thoughts are (i) acquiring and using a GW hydronic wood boiler is not for the faint-hearted; (ii) GW could do better in guidance and training for the installation process; (iii) pex tubing should NOT be used near the hotwater output; (iv) a draft inducer may be useful but does not appear essential; (v) wood consumption projected for a month would be about two full cords; (vi) feeding wood to the boiler every 3-4 hours is about the norm for the inexperienced, though after 6-8 hours it is still possible to get a good burn again, and one needs to take account of such factors as wood quality and quantity loaded, external temperature, programmes set on thermostats...
I would welcome comments and suggestions from those with more experience!
Installation proved lengthy, at about 70% of the price of the boiler. Duration of installation was due inter alia to the flow valve provided by GW not being the same as the one specified in the installation guide. Other issues involved the electrical interface with the oil-fired boiler.
After two or three successful trial runs lasting a day or two, a longer run was begun. It ended abruptly on the fifth day when the 1” pex hot water output tubing burst, which then produced overheating because hot water was not reaching the heat dissipation fan circuit. The output pipe was copper for the first 4 feet, then 1" pex, and the burst was 3 feet from the start of the pex (i.e. about 7 ft from the boiler). Simple repair, replacing pex with copper pipe. In hindsight, the aquastat controlling the fan operation may have been set too high; a lower setting might have eased the heat/pressure buildup and precluded the pipe burst.
My thoughts are (i) acquiring and using a GW hydronic wood boiler is not for the faint-hearted; (ii) GW could do better in guidance and training for the installation process; (iii) pex tubing should NOT be used near the hotwater output; (iv) a draft inducer may be useful but does not appear essential; (v) wood consumption projected for a month would be about two full cords; (vi) feeding wood to the boiler every 3-4 hours is about the norm for the inexperienced, though after 6-8 hours it is still possible to get a good burn again, and one needs to take account of such factors as wood quality and quantity loaded, external temperature, programmes set on thermostats...
I would welcome comments and suggestions from those with more experience!