OK, DV (millivolt systems) experts...I've got a baffler.
Got a customer with an older Gas Technologies, Inc gas fireplace. This company was the precursor to Heat n Glo...
Not a very aesthetic unit...Flames are all the same size & the logs are concrete...
Anyway, I digress...
Like I said, it's a millivolt system T-couple/T-pile & the unit works fine, burns nice & steady
Mv readings are 550 +/- on the pilot & 220+/- with the burner on...
Perfect, right?
Once the blower comes on, the millivolts on the t-pile drop like a rock...
I mean quickly...
Within 2-3 minutes, the burner will shut right down...
If I turn the blower rheostat off, the mvs climb back to normal...
This unit has a spill switch wired into the valve/t-pile/rocker switch system, so I rewired the the system
to eliminate any potential grounding due to the deteriorated sheathing...
Still the same results...
I took the thermo-disc out of the blower system & still the same results...
I unplugged the fan & turned the rheostat on & the mvs held true...
I turned the rheostat off & plugged the fan into the "hot" (unswitched) receptacle,
& the mvs held true...
I don't have the know-how to test the rheostat or the blower to determine which one is (or BOTH ARE) the culprit...
Any ideas where to check next?
Got a customer with an older Gas Technologies, Inc gas fireplace. This company was the precursor to Heat n Glo...
Not a very aesthetic unit...Flames are all the same size & the logs are concrete...
Anyway, I digress...
Like I said, it's a millivolt system T-couple/T-pile & the unit works fine, burns nice & steady
Mv readings are 550 +/- on the pilot & 220+/- with the burner on...
Perfect, right?
Once the blower comes on, the millivolts on the t-pile drop like a rock...
I mean quickly...
Within 2-3 minutes, the burner will shut right down...
If I turn the blower rheostat off, the mvs climb back to normal...
This unit has a spill switch wired into the valve/t-pile/rocker switch system, so I rewired the the system
to eliminate any potential grounding due to the deteriorated sheathing...
Still the same results...
I took the thermo-disc out of the blower system & still the same results...
I unplugged the fan & turned the rheostat on & the mvs held true...
I turned the rheostat off & plugged the fan into the "hot" (unswitched) receptacle,
& the mvs held true...
I don't have the know-how to test the rheostat or the blower to determine which one is (or BOTH ARE) the culprit...
Any ideas where to check next?
I'm no expert but it sounds like you are somehow grounding thru the rheostat. It only happens when the blower unit is plugged in because I'll bet the blower cord has a three prong plug on the end and when you plug it in you ground the system.