Troubleshooting Jotul GF 300 DV - Main burner and pilot light go out shortly after turning burner on

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here

JotulJohn

New Member
May 1, 2022
1
Maine
Jotul GF 300 DV - installed in seasonal use home, unit was not used for two years. This year cleaned and vacuumed main fire box burner plate, burner gas orifice, thermocouple, thermopile, pilot light assembly. The pilot light lit, stayed lit with good
flame length and color. Removed and cleaned everything in the fire box, logs, stones, and coaxial flow chimney top removed and inspected for intake and exhaust air blockages. I checked the exhaust outflow side of the coaxial flow pipe for obstructions by blowing air from a leaf blower up from the firebox (no back pressure of air) but could not think of a way to inspect or test the fresh air side for obstructions such as mice nests, wasp nests, etc. without removing a section of coaxial pipe above the fireplace unit.
[Hearth.com] Troubleshooting Jotul GF 300 DV - Main burner and pilot light go out shortly after turning burner on
[Hearth.com] Troubleshooting Jotul GF 300 DV - Main burner and pilot light go out shortly after turning burner on


When knob on gas valve was turned from PILOT to ON main burner would ignite and after 4-5 seconds there was a loud click heard and felt from the gas valve and both pilot light and main burner would extinguish. The pilot light could be relit and the main burner could be lit and then as before extinguish after 4-5 seconds. See 16 second long video.

If the front safety glass was removed the main burner would stay lit. The flame would be irregular and not all of the holes in the burner plate would have a flame.

This model Jotul has a rectangular plate on the top of the firebox that has two insulated holes that allow the plate to be held in position by two threaded posts on the left and right side of the plate. I have no idea as to what this rectangular plate is designed for, only that it was closed when the unit was previously working. I had removed and used this plate as a source of fresh air with the safety glass on the front of the fireplace installed while troubleshooting the problem.

Used a multimeter to check SIT820 resistance test between TP and TH - good test between 1.75 and 2.75 R

Checked resistance on main gas valve solenoid - good test between 0.0 - 0.2 R

Checked thermopile voltage with pilot light only lit at TH TP and TH terminals - good test about 750 mV
- With OFF/PILOT/ON knob turned to ON the mV doesn’t drop AT ALL and stays the same, about 750 mV, that is not what I expected and there was not a voltage drop. Bad test, but the gas valve opens and the burner ignites.

Some other thoughts -

The exhaust restrictor plate is wide open, could it have fallen from partially closed to fully open over the years? The restrictor plate is held in position by one screw that the plate hinges upon. The unit is free standing and has two 45 degree elbows in the axial flow pipe that connects the fireplace to the exterior of the home and the vertical run is about 12’. Using the chart the horizontal run is less than 5’ and the vertical run 12’ give a restrictor plate position C. I will need to check the device to see which setting or position the restrictor plate is set now.

[Hearth.com] Troubleshooting Jotul GF 300 DV - Main burner and pilot light go out shortly after turning burner on
[Hearth.com] Troubleshooting Jotul GF 300 DV - Main burner and pilot light go out shortly after turning burner on
 
Your mV reading should be taken between the TH-TP & TP terminals.
TP = ThermoPile. That's why you didn't see a voltage drop when
the burner side opened in the gas valve.
If your unit works fine with the glass off, it's definitely a venting issue.
he plate you're describing is a safety "blow off" plate to prevent the
glass from exploding from too much gas igniting in the firebox.
Reinstall it Before operating this appliance.
You COULD have a bad seal in the venting, allowing exhaust to get
drawn back in with the combustion air, but that would also cause the
flames to be dirty & sooting in the firebox would result.
It COULD be the restrictor, but I don't believe your short run would
result in a problem with the restrictor wide open. You can confirm
this by watching the pilot flame. When the burner ignites, the DV system
will draw more combustion air into the firebox. If this air agitates the pilot,
& it doesn't hold steady on the thermocouple, the safety valve mechanism
will shut off the gas flow to the pilot. Placing a small piece of thin aluminum
at the pilot assembly & in the path of the incoming air flow can help this situation.
 
I had a similar problem years ago when my Jotul Allagash 300DVII was just a few years old (around 2001. I eventually traced the problem to improperly crimped wire terminals on the wires that connect up to the Rocker Switch on the backside of the stove. When the terminal lugs were crimped onto the wires, the crimping person failed to strip the insulation off the end of the wire (usually requires about 1/4 inch bare wire to be inserted into the crimp type terminal). These crimps were made right over the insulation. It apparently made slight contact through the insulation; but not as much as required for a reliable crimp. My theory on this was as the heat from the stove radiated into the crimped barrel of the crimped terminal lug, it caused the barrel metal to expand and the squeezed insulation to expand and it interrupted the connection in the wires.
I had 100% success by cutting off the old crimped terminal lugs and crimping new ones on using the proper technique of stripping the insulation off the ends of the wire. There was enough slack in the original wiring to permit this to be done. You can do a visual inspection of the crimp looking into the end where the wire protruded from the terminal lug. If you see insulated wire protruding from the end of the terminal lug, where the screw hole is, then you have found a problem.
Here is a link to information on how to strip and crimp wires of different types: https://wirefyshop.com/blogs/news/a-beginners-guide-to-wire-crimping-tools-how-to-choose-and-use-them-effectively#:~:text=Place the crimp terminal with,to create a secure connection. Note; the step showing applying heat to the crimped wire is not normally done unless you are using lugs with heat shrinkable tubing or with solder inside which needs to be melted. Typically, simple crimp lugs should not be heated like that. I have made many hundreds of durable crimps over decades of work; without ever applying heat to the crimped end.
Another problem I remember encountering was the small aluminum gas feedline tp the pilot assembly. It turns out, much to my surprise that the aluminum tube is also a current return conductor to complete the circuit to keep gas on the pilot assembly. It that tube cracks due to rough handling or too many times being unfastened and refastened with the small nut at the end of the tube, it can prevent the pilot assembly from receiving gas; the main valve will not let the pilot have a gas supply if that small aluminum feedline is broken inside the fitting; and you can't see it from the outside.
 
Last edited: