We all know that storage in the conditioned space is a good thing in winter, and that it's a bad thing in summer. Likewise storage in an outbuilding is a bad thing in winter.
But how good and how bad?
Assuming:
Surface area of tank:
Heat gain with tank indoors, 110 degf deltaT:
Heat loss with tank outdoors in winter, 160 degF deltaT:
So with tank in outbuilding in winter, total heat loss would be about a 1000 btu per hour, 600 lost to the great outdoors plus 400 not gained indoors. My heat load in winter averages about 25,000 btu per hour, so for me having storage outside the house would be like throwing away 4% of my fuel. Hurts some, but not the end of the world.
In summer the only disadvantage to having storage inside is heat gain, on the order of 200 watts, or about 0.06 ton of refrigeration.
So my conclusion is that these are pretty small numbers. If you need to put storage in an outbuilding, insulate well and don't look back. If you can put storage inside, so much the better.
And if you're using indoor storage for DHW in summer you won't be sweating because of it.
But how good and how bad?
Assuming:
- 1000 gallon LP tank, 41 inches in diameter and 194 inches long, 180 degF
- inside temperature 70 degF
- outside winter temperature 20 degF
- R-50 insulation
Surface area of tank:
(2 * (pi 20.5^2) inch^2) + (41 pi 194 inch^2) = 191.87 ft^2
Heat gain with tank indoors, 110 degf deltaT:
191.87 ft^2 * 110 degF / 50 Rvalue = 123.71 watt = 422.12 btu / hour
Heat loss with tank outdoors in winter, 160 degF deltaT:
191.87 ft^2 * 160 degF / 50 Rvalue = 179.94 watt = 613.98 btu / hour
So with tank in outbuilding in winter, total heat loss would be about a 1000 btu per hour, 600 lost to the great outdoors plus 400 not gained indoors. My heat load in winter averages about 25,000 btu per hour, so for me having storage outside the house would be like throwing away 4% of my fuel. Hurts some, but not the end of the world.
In summer the only disadvantage to having storage inside is heat gain, on the order of 200 watts, or about 0.06 ton of refrigeration.
So my conclusion is that these are pretty small numbers. If you need to put storage in an outbuilding, insulate well and don't look back. If you can put storage inside, so much the better.
And if you're using indoor storage for DHW in summer you won't be sweating because of it.