It doesn't take much of a layer of scale to really start hampering HX efficiency. If hard fill water is added on a regular basis, and the furnace is run at bhigh temperatures you will need to de-scale the system more often.
It will take a lot of product to treat that volume of water. If in fact you fill water is hard, above 12 grains or more, you might consider re-filling with DI water after you clean the system.
You can purchase DI water, take some plastic 55 gallon barrels, or rent a DI tank for a day.
Man
Did you check the hardness of the fill water. If you have a limescale build up, it is from the water you are filling and adding. Also the hotter you run the system, the more mineral will precipitate and coat the surfaces.
With that much fluid in the Heatmor you will need a bit of cleaner, so a strong acid, diluted as per the directions on the bottle, would be my choice.
Ideally you would refill the system with DI water. You can purchase DI water, take a few plastic barrels and they will fill them. Or in many areas you can rent the DI filter, connect a hose and fill the system.
In my area Culligan will rent the DI filters, or sell the water if you drive to their location.
I would also add conditioners for corrosion protection to the fill water, being an open system it will always take on O2. The inhibitors are to scavange the O2 before it corrodes the ferrous components. Adding inhibitors it will be an ongoing ritual.
Here is a chart showing how a very thin layer of build up hampers HX performance. Both at the OWF and any HXs in the system.
We had a GEO expert present a webinar on Fluid Quality a few years back, here is the DI unit he fills his systems with. The light indicates when it needs to be re-beded.