jimde said:
I contacted Bioheat and one of there support people stated that I should definetly go with parrallel piping of the tanks. I dont know why,but that is what he said.
I'm assuming by parallel piping both yourself and the support staff are referring to multiple tanks standing side-by-side literally parallel to one another, with a manifold across the bottom and one or more manifolds across the top. I believe the advantages of this type of configuration are that columns of water can stratify well, and they can be built in unit sizes that will fit through doors. One disadvantage could be that if you pipe the manifolds incorrectly the tanks may not all be fully utilized because flow is directed preferentially. Another is the possibility water jetting might destroy stratification and mix cold and hot water.
With standing tanks the other possibility would be tanks in series with the top of one tank piped to the bottom of the next and so forth. I've only seen this type of arrangement described in solar-hydronic tank batteries. With two ports on each tank I'm speculating that the advantage might be that solar-heated water of various temperatures could be introduced into the storage tanks at the point where such temperature best belongs at the time. But this is just speculation on my part, and at any rate I'm assuming this is not what you want for a solid fuel boiler storage system if for no other reason than none of the boiler manufacturers says to do it this way.
With multiple horizontal tanks laying one above the other you'd have to call it series piping because water has to go all the way through one tank to get to the other, whether it be hot water from the boiler filling from above or cold return water from the load filling from below. Here you know that even if water is getting stirred up by jetting into one tank, at least stratification isn't being disturbed elsewhere as long as the ports between the tanks are big and lazy. And whereas propane tanks are sometimes cheap and plentiful, horizontal series tanks may simply enjoy the virtue of necessity, since typically ten foot long 500 gallon tanks hayna going in there any other way.
To me the stacked multiple horizontal tanks in series seems more foolproof, but that may just because I don't understand the subtleties of setting up parallel vertical tanks yet.
[See below where 2.beans demonstrates that horizontally oriented tanks can be at the same elevation and piped in parallel same as vertical tanks at the same elevation. And he's got some nice shark-repellent data from the lab to end any speculation as to whether it works or not.]
It sounds like you already have your tanks, and very nice ones at that. Since they are vertical tanks you will be piping them in parallel and it won't matter what you might otherwise have preferred except for the purposes of discussion. But not to worry since from everything I've read vertical tanks in parallel could arguably the best way to go and are in no way inherently problematic.
If you have head-space to work with
it seems to me it would probably be worthwhile to do what it takes to get the tanks as high above the boiler as practicable so that with appropriate free-flow check valving the system will therm-siphon without pumping in the event of power failure, without having to get into the whole dump-zone thing. [This seems inherently safe to me, if I've got this wrong I would much appreciate it if someone could let me know sooner rather than later.]
He also stated that I will have to go with a larger than average pump to make it to the furnace 170 feet away.
Average pump has nothing to do with it. What you need is what you need according to what your situation is and what your design goals are. Anyway this is a separate pump that doesn't affect your storage tank piping if that's what we're talking about.
I dont understand what the XX and YY means.
Sorry about any confusion introduced by this topic. In one particular set of schematics there are some confusing footnotes about XX and YY piping. AFAIK the XX and YY points are not standard terms-of-art so don't worry about it
Another question I have is should I purchase a termovar loading unit. I already have the termovar mixing valve that I could use for the infloor zone. Would it be worth the money for the loading unit for the house heat zone? Any information will help.
[Re-reading your question it seems you might be asking whether it would be worthwhile to mix down the temperature supplied to radiators, wall panels, or baseboard loops once the hot water arrives from the 170 ft transport loop. I don't see how this would be desirable, let alone worthwhile, but others disagree.
If you're asking should you mix down the temperature of the water fed into the 170 ft transport loop, absolutely not. The heat capacity of the transport loop is delta-T times gpm. If you need less capacity use smaller, less expensive pipe or reduce gpm.]
For any solid fuel boiler I'm aware of, you absolutely must provide some means of getting the boiler water jacket up above 140F to 150F (or whatever temperature depending on the particular boiler) as quickly as possible and keep it there. The most common way is to provide a big thermostatic mixing valve that keeps the boiler return temperature hot enough by mixing recirculated boiler supply water back into the return port. The Termovar and Laddomat units incorporate such a thermostatic valve along with a circ pump and a special free-flow check valve all in a nice package.
Another option involving thermostatic valves is to use discrete components. In this case by far and away in the U.S. market the most popular high Cv mixing valve appears to be a Danfoss valve designed just for this purpose.
Also you could use a boiler recirc circuit and then use an electronically controlled variable speed pump in the boiler-to-storage-tank circuit to introduce cold return water at just the right rate to maintain high enough boiler temperature. Have a look at the Caleffi hydronic separator to see how this might be done.
Cheers --ewd