Is co2 heat storage tank possible?

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

acavanagh

Member
Hearth Supporter
Aug 6, 2008
47
Lakes Region, Maine
An opportunity just came up where I can buy a ~1,500 gallon co2 tank that was apparently used by the miitary. I think it must be over 1,000 gallons, but am not sure because the thing just says it is 5 tons. I was planning on using a 1,000 gallon propane tank, but this will be about half as much and is already insulated and jacketed. It has a release valve at the top accessed with an attached ladder and a few pipes coming out one end. You can't actally see the tank as it is insulated and then covered with a steel metal jacket . The whole thing is shaped like half an oval. It must be about 7 feet tall and about 14 feet long. It looks like it is in great shape as it was stored indoors. Apparently there is some new code and they are replacing some of their older tanks. I understand that propane tanks are welded and designed to take pressures in the hundreds whereas co2 tanks are seemless and can tank pressures in the possible 1,000's. Would there be any problems with this type of setup if I use it for heat storage for my EKO60? The guy is thinking about scrapping it, but he wants it out soon, so I need to have an answer for him before the snow starts falling as he puts it. Any help would be appreciated.
 
Seems to me it would work, probably with some welding for appropriate fittings. Radius x radius x 3.14 x height (all in feet) will give you cubic feet of tank, take that x 7.48 = gallons of water. Sounds like it's pre-insulated, too.
 
I di the calculations before, and it is anywhere from 1,000 gallons to 1,500. Not sure as I can't really see the tank. There must be about 10 inches of insulationg surrounding the tank and then steel covering the insulation. From what I understand, these co2 tanks are like big thermoses. They seem to be perfectly suited for this applicatoin. They are much thicker than propane tanks as well. I am just worried that I am missing something. I haven't heard of one being used for this application. Structurally would there be any problems with converting a large co2 tank to holding water at temperatures around 200 degrees. I don't want this thing exploding on me or cracking. I also wonder about having the piping all on one end of the tank. I know that the large propane tanks used for storage have multiple fittings on the top. Will having all the fittings on one end restrict the heating of the water? It seems like it would work. The thing is enormous though. It weighs about 5 tons compared to your average 1,000 gallon propane tank at 1 ton. I was planning on putting on an attached garage within a few years. Would keeping this insulated tank for heat storage outside piped underground make sense until then? Not sure of the heat loss on a well insulated co2 tank. Any thoughts.
 
I would advise you to look for the tank nameplate data. To me this sounds like a cryogenic type of tank where the product was kept cold, therefore the pressures were much lower also. I find it hard to believe that tank could hold thousands of psi though with the military who knows. If you look at the ASME code for pressure vessels the wall material gets very thick very quickly at much lower pressures when the the tank gets big. I use to deal with a liquid nitrogen tank of about the same diameter but it was only operated at 50 psi and the pressure bled off as the N2 was used. The CO2 tank may just be thermos style contstruction as the N2 tank I mentioned-inner tank-vacuum-outertank. I wouldn't give up on it-you may have a real quality tank for a steal. Just be sure to know what it is rated for. That nameplate data is hiding somewhere.

Mike
 
I know it is co2 as the guy who has it now was there when they let the gas out. The pressure gauge on the side goes up to 2000 psi as I recall. Not sure what it is rated for though. I honestly didn't see anything showing that. I talked with some people who thought that it was probably used to extinguish fires, as it was used by the military and they said that they would use large quantities of co2 all at once.

I talked with Mark at AHONA and he seemed to think it would be perfect. I think I might just bite the bullet on this one. For the price, size, insulation, and the thing has a cool history, good conversation piece. I just don't want the thing to blow up. I just wasn't sure if they would fit this application.
 
Thanks Mike. I am worried about the pressure for heat as well. I am positive the insulation was to keep it cold as is the case for co2. I worry about that expansion. I haven't found much information on this. This is an all new thread on heat storage. We are crossing a new frontier here. I know the new co2 tanks are rated for temperatures ranging from -45 degrees celcius to about +45 degrees celcius with pressures much higher than propane. I know with co2, if the refrigeration goes bad that they bleed off, and one would think they build in some room for extra pressure as a fail safe. I am wondering if there is anyone out there who has a co2 tank used for heat storage.
 
If it is made for cold temps you might want to make sure the insulation will be ok at 100*C.

Also, regarding the question about all of the fittings going in at the same place, maybe you could put a long pipe into one of the fittings and attach it to the fitting so that water going into or out of that port would actually be going into or out of the tank from the other side.
 
Andrew - given the low pressure you are going to subject it to (assuming you are using pressurized storage), you should have nothing to worry about with respect to the tank's original performance specifications. However, do you know what it has been used for since it was taken out of service? Is there corrosion in the tank? Residue from storing something else? A CO2 tank will be clean as a whistle since oxidation cannot take place within the tank while it is filled with plain CO2. However, once O2 gets in there, corrosion can begin.

Sample the insulation and heat test it. I strongly suspect you will find that it is closed cell polyurethane, and you should be just fine. I just tested some plain old EPS (styrofoam) board that I am using in some places around my GARN and I could not melt it in a pot of boiling water.

Post some pictures of this puppy!
 
First, let me just say I love this site. It seems we all have a common interest in finding new and imaginative ways to save money on heating. I am cheap by nature, so I love this.

Free75, that is exactly what Mark at AHONA mentioned in regards to the piping. Great idea!

Jim, if I end up getting it, I promise to post a picture of this beast. A picture is worth a thousand words right. The insulation, at least the visible stuff that you can see around the release valve at the top of the tank is actually a type of blanket insulation. Of course, not actually seeing the tank, the tank itself may be coated with a foam type insulation. Not really sure. There must be about 10 inches of this insulation around the tank. I have heard of just taking batt insulation and wrapping it around a propane tank to insulate it, so I don't see how this will be a problem. Though I have never done it myself. I do know that the tank was used for co2 until it was decommissioned recently. I guess if it wasn't for a change in some code of some sort they would still be using this monster. It looks clean on the outside, and like I said, the guy who currently has it was there when they emptied it. From there it was brought to his place and that is where it has sat since, unused.

The guy had another co2 tank taken from the same base that had no steel shell and the foam insulation scraped off the outside, that is about 2,500 gallons that he is giving to his brother to be used as a septic tank at a golf course. That one I could see inside, and it was very clean. It also was extremely thick. Seriously thick. Close to an inch thick. As the guy said, you could stick this thing in the ocean for a few years and it still would hold pressure.
 
I'd pick it up in a heartbeat. Steel tank that will work as a pressurized system with insulation already installed. Excellent buy if its cheaper than you can get propane tanks for.
 
Just to let everyone know in case people were wondering, the deal fell through. Haven't heard from the guy. Its probably a good thing too, because we were initially going to put it into a garage. We have decided we aren't going to build the garage anytime soon, so the tank would have been an eyesore in our yard indefinately. Also, from what I have been learning, for DHW, pressurized tanks seem to be a little trickier. We have actually decided to go with unpressurized due to the problem of having to fit a heat exchanger in a tank. I liked the idea of pressurized, but it gets tricky when you try to heat your DHW. So, I have been converted from pressurized to unpressurized.

Is it possible to have a hybrid system whereby you can use both, say a 500 gallon pressurized tank and an open tank together. Of course the open tank shouldn't be allowed to have water temps over 175 degrees. I was wondering if it would be at all possible. I am thinking it wouldn't be since the tank temp can only get as hot as the boiler. If the open system can only allow temps of up to 175 degrees, then how would the boiler know the difference? I am thinking you would need to have some serious controller on there. Has anyone heard of using them together, pressurized and unpressurized?
 
Andrew04039 said:
Also, from what I have been learning, for DHW, pressurized tanks seem to be a little trickier. We have actually decided to go with unpressurized due to the problem of having to fit a heat exchanger in a tank. I liked the idea of pressurized, but it gets tricky when you try to heat your DHW. So, I have been converted from pressurized to unpressurized.

I don't understand why you say it is harder with a pressuized system. All you need is a sidearm or hx the same as an open system. I've had both and I'm using the same setup with my pressurized system. You can't run or mix you DHW with the boiler or storage water so you use some type of hx.
leaddog
 
I guess harder in the sense of getting enough surface area in the tank with a heat exchanger, coil or other means. I want to make sure hot water isn't a problem and I worry about getting enough heat transfer by means of stuffing something in a small opening in the tank. I am not saying that it can't be done, I am just saying that for DHW, the open system seems a lot easier and straightforward. My biggest fear would be not having enough hot water for showers etc. and the wife going ballistic. I have seen other people switch from the idea of pressurized to unpressurized when it comes down to the DHW situation. Beleive me, I went kicking and screaming as I had my heart set on a pressurized type system. I think it is a lot cleaner, and the direct tranfer for heating the house appealed to me, not to mention the price. What type of heat exchange did you use in your pressurized system? How did it fit inside the tank. What kind of surface area do you have? The opening on say a 500 gallon propane tank can't be that much, and that is what we were considering, two 500 gallon propane tanks. (Actually we were considering a 1200 to 1500 gallon Co2 tank that probably had a fairly sizeable opening for getting a heat exchanger in. The problem with it is that it would need a home and the beast weighed in at 5 tons.)
 
Andrew04039

Why not just weld a 1.5" port into a pressurized tank, and insert a copper-coil HX? You can run fresh water through it, either directly to your hot water system, or to your existing hot water heater? These HX's are available, and run about $300. You will have essentially unlimited DHW, as long as you are running the wood boiler. Use the existing DHW heat source as the backup. I think that setup would be just as easy as an unpressurized system, and probably similar in cost. You can go either way - pressurized or unpressurized, that is your call. However, the DHW can be taken care of just about the same either way, so that shouldn't necessarily be the deciding factor.
 
I picked up a 80gal tank with a copper coil in it and just run my zone from the storage there but you can use a sidearm with your elect or gas waterheater and that is useually enough but if you really use ALOT of water at a time you can put two in . Hot water tanks are really cheap if you watch for them. People are always changing them out and as long as they don't leak you are good to go.
Pressure systems are the best way to go.
leaddog
 
Boilerman,

How much coil can you fit in a pressurized tank using a 1.5 inch hole. How much length? How much surface area?
I just worry about getting enough heat from the heat exchanger in the tank. I know with the open system, you can easily put in lots of coil that encompasses most of the tank to get as much heat out of the water as possible.

Leaddog,

I considered that option as well. I know the tank we have has very little piping in it. It is a 40 gallon tank. Not exactly sure of the coil length, I know it is steel. I have heard that they are about 5 to 15 sq feet of surface area generally. 120 feet is more in the 30 to 35 foot range and am told should be plenty to pull heat out of the tank. I just worry about the complexities of adding another tank on top of the two 500 gallon tanks we would add. How many feet of coil are in your 80 gallon tank? How would you pipe two tanks together, for instance, an 80 gallon tank and the existing 40 gallon tank? Is it as simple as I think it is, just putting the outflow into the inflow on the second tank?

The cost difference for me isn't that great to make me really want to go through the headache of getting the tanks and getting them in the house and the headache of finding someone other than me to hook them up, if there is a qualified installer willing.

There are a lot of ifs in there for me to go with the pressurized storage. The unpressurized tanks take that out since they are ready made. They are light enough to carry into the house. I do worry about the complexities and the DHW. Not many installers are familiar with the pressurized storage as well. The unpressurized systems seem to be more common and so the installers are more familiar with them, and long term if anything goes wrong, a plumber or the installer will be able to help me out.

I wish there were kits for the pressurized systems utilizing old propane tanks for cost savings. It really sucks, but just finding an installer in my area that seems to understand these systems has been a headache in and of itself. I just have been beaten down so much by this process that the prospect of having to get two large propane tanks into my basement and the headache of finding a qualified installer willing to hook them up does not appeal to me. I am shocked at how few plumbing/heating professionals in Maine there are that are licnensed for solid fuels, and how few of them are familiar with wood gasifiers and willing to hook them up. This is technology that is not new, and really should be embraced. Its quite sad that Europe is kicking our butts on the prevalence of these systems. I'll get off my soap box now. This has turned out to be quite the message. :)

Leaddog you almost had me back on the pressurized bandwagon, but I just don't want to deal with the headaches. If two 500 gallon tanks fell on my lap, well I guess I might try harder to go that route. I am curious how you did it though with the 80 gallon tank. Any issues of DHW when the boiler isn't running? What temp of storage do you need to make the temp for hot water sufficient?
 
My 80gal tank I picked up at a yard sale. It is stainless and come out of a hospital. I don't know how much coils are in it but I can't run it out of hot water if I'm running 180* water in. It is insulated. As far as a sidearm I know several people that have them hooked up to there waterheaters and they are happy with them. If I was to use two tanks I would just put a side arm on each. You do need a tempering valve to limit the temp coming out to 120* but that adds to the amount of hot water avilable. search sidearm here and there is several threads on them
leaddog
 
We don't have a problem with our 40 gallon tank with temps at 180 with the oil boiler running. The problem we are foreseeing is during the summer, with storage, we want to make sure we aren't having to charge it every day. I am told that with 120 feet of coil in the unpressurized tank, that the water coming out is almost the same as the temp at the top of the tank. So, conceivably, temps in the tank could get pretty low before you lose your hot water.

I took your advice and read a little about the sidearms, but how much heat exchange do you get from them? It acts as basically a shell over the pipe for your hot water heater. Am I right? Basically a small storage tank with the hot water pipe acting as a heat exchanger. The diagrams I have seen are basically a larger pipe running the DHW to the tank and the sidearm running heated storage/boiler water through it. Is that the principle? How much heat can that sidearm pull from the storage water? It just doesn't seem like enough surface area to pick up enough heat for DHW. Most coils they recommend quite a few feet to effectively get the heat out. That sidearm just doesn't seem like enough.

Our problem for storage is mostly during the summer for DHW. We want more time between burnings. I should say I want more space between burnings since I will be the one doing it not the wife. The unpressurized system can store water at 175 degrees safely for the liner. That gives us 1200 gallons of about 55 degrees to work with down to the 120 degree water temp. That should buy us lots of time during the summer. Also during the spring and fall. If a sidearm can be had for fairly cheap and is as effective as 120 feet of coil, then I can see the benefits of pressurized over the unpressurized in that you can store water at even higher temps. Then we might be looking at 80 degrees of play with 1000 gallons.

The problem I see is an "easy" way of heat exchanging the storage tank for DHW.
 
The difference is with a large coil you are pulling the heat off as you use it where with a sidearm you are storing the heat in a 40 or more gal tank. How often do you use 40gaql of hat water at one time, and if you have it higher than 120* you have more than that as you are mixing it with cold water to get it to 120*. My stepson has one on a 50gal tank and he said he has run it down to just under 120* acouple of times but they were drawing water for a HOT bath, doing dishes, doing laundry (rinsing dishes with HOT water).
As far as the summer is concerned I put my pump on a timer and run it 3 times a day and circulate it for a half an hour and have all the hot water I need.
leaddog
 
We use a lot of hot water. Not sure how long 40 gallons would last. Not sure how long 80 gallons would last. I don't think 40 or even 80 gallons would last much more than a day. I see what you are doing though, having it circulate every so often to ensure the temp in the hot water heater is about the same as your storage tank. How hot can a hot water tank get? I know pressurized storage tanks are about 200 degrees, but say a DHW tank, is that too high? Would you need some sort of regulator to make sure the temps entering the hot water tank are not above a certain max? I see what you are doing now though. Interesting. So the sidearm is just circulating storage tank water through the hot water tank to get it up to temp? Is that an oversimplification or what.

Your method of cycling definately takes care of the issue of running out of stored DHW. I like your method better than running an exchanger in the tank itself. How do you have the cycles timed. I didn't know you could do that. Could you have a circulator kick on if the temps got down to a low amount?

Damn I like it because you can store higher temps. I still have the problem and headache of finding someone to actually hook it up. Around here, if you want to hook up the pressured storage tank, you pretty much have to do it yourself.
 
The way a sidearm works is the boiler water circulates through a copper tube and the DHW from the waterheater circulates thru a tube inside. With the boiler water circulating say at 160* it enters the top of the sidearm and exits the bottem. this must be pumped. The waterheater water enters the bottem from the bottem of the waterheater tank. The hot water then exits into the top of the waterheater. This water doesn't need to be pumped as it will thermosyphen, hot water rises. As you draw hot water the cold water from your water source will travel to the bottem of the hotwater heater and will then be heated up in the sidearm. This isn't fast but it does work well and most people are satified, and alot of people are useing it. In the summer I just use a cheap timer and run my pump early in the morning, afternoon, and evening and that covers my useage. That can be to adjusted to your use. As far as hooking it up it is easy to do, just ask and I'm sure you will be guided here.
leaddog
 
Thats what I thought. Thanks for the explanation leaddog.

I guess there is no way of knowing if your water usage will be greater than the time it takes to heat it up. Unless you are well versed in thermodynamics. I worry that our usage, although in a given day may not be huge, may be very high at times. Both my wife and I take long showers, we have a dishwasher and are guilty of rinsing dishes with hot water without shutting it off between dishes. I also have a tendency to run hot water nonstop when shaving. We really suck at hot water conservation, and that obviously would be the easy answer, but I don't want to have to worry. Wood is cheap. So my biggest fear is that the DHW will be under too much stress to be compensated by the exchange surface of the sidearm.

The thing is I personally am the type of person that can stand it even if it isn't and add another hot water tank or whatever until it is right at my liesure. My wife, god bless her, is the type that will give me holy hell if her shower gets cold. I'll never hear the end of it.

So I thank you for the info leaddog, maybe I can convince my wife to wait on the storage until I can find cheap tanks and an installer willing to hook them up.
 
I have a 1000 gallon unpressurized storage tank with 120 ft of 3/4 copper pipe for DHW. The water temperature can get down to 120 degrees and I still get all the hot water that I need. In the summer I run the Tarm for one day to reheat the tank and get a weeks worth of DHW. The nice thing about this is that the water temperature is constant, you never have to fiddle with the water temperatur when taking a shower. I will be heating the water to 175 instead of 185 degrees since my rubber liner deteriorated after 7 years of use. Hopefully I can still get a weeks worth of DHW at this lower start temperature.
 
Brialin,

That is what we are considering, and I have heard good things about it. I would suggest keeping to the maximum suggested temp of 175, since I have heard many stories of deteriated EPDM at even 185. It sounds like you are one of them. Although honestly, at about only $200 for the liner, that extra 10 degrees gives you a lot of stored BTU's with a 1000 gallon tank, but I have never changed a liner, and I am sure it isn't exactly quick and easy, so wasting liners every 7 years although not too much money, might be a pain in the @ss. So a days burn, is that one burn or a few burns in the day? A weeks worth is awesome, that is what I am looking for, and no more than one burn a day in the winter. The open tanks seem simple and straightforward, and more do it yourself since you can self assemble due to lighter weight, but they are pricey especially after all the coils. I like the idea, just not the price. The tank we are looking at would cost us about $4500 for everything but the install. I think most of the people with pressurized systems paid little or nothing for their tanks, so price wise, there is no comparison.

We just got a quote from a place in Portland ME this morning. I worry that they are charging too much since the quote for the materials alone for the boiler and storage installation was about $8500. To me that is crazy since they quoted their tank package at about $4500 for materials with the self assemble, that is the tank with liner, and 4 120' coils. That leaves about $4000 for a few valves a circulator a few odds and ends and some piping. That seems crazy to me and I am seriously questioning the integrity of the installer. To me you pad labor, not materials and I already feel they are padding labor.
 