Hi Y'all, really hoping someone can help me..
So I've been on this forum before, trying to resolve my draft issue, and I've made some investigative progress...
I have a jotul f55 installed in the basement, goes up 2ft single wall to a 90, then into the brick external chimney to double wall insulated pipe, another 90 and upward 20ft.
I had my draft tested finally;
about 25deg outside, breezy
With air control totally open and a pretty good fire rolling, draft measure 11-12 (im guessing 0.11-0.12?) the technician was saying "eleven-twelve") and with my air control totally closed, was about 5-7. I've read and been told i don't want any more than 3 with it closed down.
Technician suggested a barometric damper, so he installed it and it made a great difference.
Later that evening, i was burning and my flue remained very cool (<250 18" above stove) and i began to research, and it sounds like these barometric dampers are a NO-NO for wood stoves??? Did I hire some jackoff to do my stove??? He was certified and licensed!!
I've read they can cause excessive creasote buildup as well as be detrimental during a chimney fire
How can I better control my draft/fire in this stove?
on the bottom of the stove, if I close air control "totally", there are two 1/4+ inch gaps remaining on the "sliding gate" and there is a half inch drilled hole that is non adjustable. If i use my finger to plug the hole, i have great control of the fire then.
Would i void any warranty or cause legal issues if i somehow block the hole? Maybe with a heat rated magnet?
I'm getting 3 hour burn times on a full load and it turns into a blast furnace without the barometric damper, but the damper seems like a safety hazard! Help!
the video is the stove WITHOUT the barometric damper, with the air control totally down and a 2/3 full load of seasoned ash...
thanks I'm advance!
Matt
So I've been on this forum before, trying to resolve my draft issue, and I've made some investigative progress...
I have a jotul f55 installed in the basement, goes up 2ft single wall to a 90, then into the brick external chimney to double wall insulated pipe, another 90 and upward 20ft.
I had my draft tested finally;
about 25deg outside, breezy
With air control totally open and a pretty good fire rolling, draft measure 11-12 (im guessing 0.11-0.12?) the technician was saying "eleven-twelve") and with my air control totally closed, was about 5-7. I've read and been told i don't want any more than 3 with it closed down.
Technician suggested a barometric damper, so he installed it and it made a great difference.
Later that evening, i was burning and my flue remained very cool (<250 18" above stove) and i began to research, and it sounds like these barometric dampers are a NO-NO for wood stoves??? Did I hire some jackoff to do my stove??? He was certified and licensed!!
I've read they can cause excessive creasote buildup as well as be detrimental during a chimney fire
How can I better control my draft/fire in this stove?
on the bottom of the stove, if I close air control "totally", there are two 1/4+ inch gaps remaining on the "sliding gate" and there is a half inch drilled hole that is non adjustable. If i use my finger to plug the hole, i have great control of the fire then.
Would i void any warranty or cause legal issues if i somehow block the hole? Maybe with a heat rated magnet?
I'm getting 3 hour burn times on a full load and it turns into a blast furnace without the barometric damper, but the damper seems like a safety hazard! Help!
the video is the stove WITHOUT the barometric damper, with the air control totally down and a 2/3 full load of seasoned ash...
thanks I'm advance!
Matt