With the housing market being what it is my wife and I have decided that it is likely in our best interest to stay in the home we purchased in 2008 until we retire. We had thought of moving for more property and to be "out in the woods" as well as to a larger home, but expanding what we have will make a lot more financial sense. The plan is basically to add a master suite by converting our existing attached garage to living space (I get a 25 x 30 pole barn out back as compensation ). At the same time I want to reside the house, seal it up well, add a considerable amount of insulation in the form of foam board (see here: (broken link removed to http://www.buildingscience.com/documents/information-sheets/high-r-value-wall-assemblies/high-r-wall-12-exterior-insulation-finish-systems-eifs-wall-construction?topic=doctypes/enclosures-that-work/etw-high-r-value-enclosure-assemblie) ), and finally seal up the attic and apply blown cellulose. The goal will be a very tight, well insulated, simple box (basically a 24 x 50 rectangle). Total square footage after the conversion will come in at just a hair over 1200SF, so it will still be a fairly small house.
Right now we have forced air oil heat supplemented by the Englander furnace, but we want hydronic for a lot of reasons. The Englander is great and keeps us warm, but we hate the dust and dryness that is inevitable with forced air heat in the winter time. Also, the heat is very uneven due to a poorly designed distribution system which creates even bigger problems in the summer as the AC is barely adequate. What I'd like to do is install a hydronic system from scratch using wall panel radiators in each room. The air handler for the AC would be moved to the attic and a new dedicated ductwork system would be installed there with registers in the ceilings. The AC ductwork would be sealed and wrapped in insulation and then buried in the cellulose for maximum efficiency.
I did a heat loss calc (Using Built It Solar's calculator) assuming good tight air sealing, R-20 walls, and an R-50 ceiling, and came up with a design heat loss of 22,339 BTU/hr. As I understand it in terms of square footage and BTU/hr this is awfully small and not a large heat load compared to what the new boilers can do. That said, I do want to also ditch my electric water heater and supply all DHW via the boiler, so obviously that will be an additional load in the winter and a small load in the summer. Given the parameters, how would you design a system for this house? Just to recap:
1200SF
Design Heat Loss: 22,339 BTU/hr
All DHW supplied by boiler
System would consist of ten wall panel radiators plus heat exchanger for DHW
Oil fuel
Would like to incorporate pressurized storage
I have looked a bit into combination wood/oil units and haven't been all that impressed, but the thought of having to buy two boilers at once is a bit daunting also. Looking forward to hearing from those much more experienced and smarter than I on this subject...
Right now we have forced air oil heat supplemented by the Englander furnace, but we want hydronic for a lot of reasons. The Englander is great and keeps us warm, but we hate the dust and dryness that is inevitable with forced air heat in the winter time. Also, the heat is very uneven due to a poorly designed distribution system which creates even bigger problems in the summer as the AC is barely adequate. What I'd like to do is install a hydronic system from scratch using wall panel radiators in each room. The air handler for the AC would be moved to the attic and a new dedicated ductwork system would be installed there with registers in the ceilings. The AC ductwork would be sealed and wrapped in insulation and then buried in the cellulose for maximum efficiency.
I did a heat loss calc (Using Built It Solar's calculator) assuming good tight air sealing, R-20 walls, and an R-50 ceiling, and came up with a design heat loss of 22,339 BTU/hr. As I understand it in terms of square footage and BTU/hr this is awfully small and not a large heat load compared to what the new boilers can do. That said, I do want to also ditch my electric water heater and supply all DHW via the boiler, so obviously that will be an additional load in the winter and a small load in the summer. Given the parameters, how would you design a system for this house? Just to recap:
1200SF
Design Heat Loss: 22,339 BTU/hr
All DHW supplied by boiler
System would consist of ten wall panel radiators plus heat exchanger for DHW
Oil fuel
Would like to incorporate pressurized storage
I have looked a bit into combination wood/oil units and haven't been all that impressed, but the thought of having to buy two boilers at once is a bit daunting also. Looking forward to hearing from those much more experienced and smarter than I on this subject...