Need help, Losing heat and think chimney is installed wrong

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.

searle7

Member
Feb 29, 2016
10
Idaho
Hello all,

I am building a new construction house and had a kozy heat Albany ZC fireplace (similar to their Z42). Local fireplace shop installed it. I posted earlier about venting the chaise until I realized the attic insulation shield has a big "vent" in the top of it already which dumps the heat into the attic. See attached pictures. The pipe on the left is the pipe from a basement gas fireplace. The pipe on the right is the outside combustion air intake. Someone in a previous thread mentioned of putting an "airtrap" as the original installers didn't do it. I verified in the manual and it did recommend it so I rerouted the pipe to include a small "trap".

I have most of the house sheet rocked and have been heating the house with the fireplace along with some electric heaters. However I don't know how I'm going to seal the chaise to prevent the house air from escaping from the attic shield 24/7 even when I am not burning. From doing some research, it seems that I'm suppose to have either a ceiling support box or a firestop? Can the firestop be caulked to prevent air leakage? Its aggravating I spent all the time air sealing all the electrical penetrations to only have this gaping hole in the ceiling.
Can anyone give me recommendations or if I am indeed missing something?

Thanks,

Austin

[Hearth.com] Need help, Losing heat and think chimney is installed wrong [Hearth.com] Need help, Losing heat and think chimney is installed wrong [Hearth.com] Need help, Losing heat and think chimney is installed wrong [Hearth.com] Need help, Losing heat and think chimney is installed wrong
 
Installation looks legit to me
 
Just wait and see...

...many newer houses are so tightly sealed wood burners question if stoves have sufficient draw.
 
It should have a fire stop on the bottom, with the insulation shield on the top side of the plywood draftstop. Then the small gap between the pipe and fire stop gets caulked to air seal it.
 
  • Like
Reactions: savageactor7
It should have a fire stop on the bottom, with the insulation shield on the top side of the plywood draftstop. Then the small gap between the pipe and fire stop gets caulked to air seal it.
Bingo. You are right. I called Metal fab Inc, the vent system used and they said the same thing. Sad thing is even the inspector didn't notice anything wrong. This is after my fix.
[Hearth.com] Need help, Losing heat and think chimney is installed wrong
 
I question the air intake. Won't that act as a chimney? I thought intakes should not be run veritcal...especially for that length.
The pipe on the right is the outside combustion air intake. Someone in a previous thread mentioned of putting an "airtrap" as the original installers didn't do it. I verified in the manual and it did recommend it so I rerouted the pipe to include a small "trap".
 
I question the air intake. Won't that act as a chimney? I thought intakes should not be run veritcal...especially for that length.
I noted that in the previous thread too. According to the OP the manual says it's ok for this appliance. I'm surprised about that, but can't argue with the manual.
 
I noted that in the previous thread too. According to the OP the manual says it's ok for this appliance. I'm surprised about that, but can't argue with the manual.
See picture. It states that if the intake is above the intake collar that an air trap is required. My guess is to prevent the chimney draft effect.

[Hearth.com] Need help, Losing heat and think chimney is installed wrong
 
  • Like
Reactions: stoveliker
See picture. It states that if the intake is above the intake collar that an air trap is required. My guess is to prevent the chimney draft effect.

View attachment 293328
Maybe I am overly cautious, but I would be 100% sure before you enclose the wall. I don't read this the same as you do. I see about adding the trap but I also read 'run to the nearest outside wall'. I don't see anything about going up through the ceiling. I could be wrong.....I have been before. Just my 2 cents.
 
The 4th pic in that page of the manual shows an air intake above the stove, and the required air trap.
I'm as surprised by you. But can't argue with the manual.

OP: the stove is UL listed, right? I think that means it'll have to have been tested including this configuration.
 
I probably am wrong. Sorry about that.
Here is the complete wording of item #4 from the manual. Can't read from the OP post about 'terminate intake at least 3 feet below termination level of chimney.'

4. If ducting beside the chimney chase, terminate intake air at least
3’ (914mm) below the termination level of chimney. The air pipe
may also be ducted below floor level of the fireplace, providing it
is ducted to the outside
 
Weird indeed. Only case I am aware of that this is (seems to be consensus) allowed.