New hydro air system
hondaracer2oo4
414
Canterbury NH
So a little background. Heating a 220 year old 2800 sqft colonial in New England. I am currently heating with a hardy h4 boiler built in 1991. Current set up in the house is a lay down oil furnace circa 1985. I have a water to air hx in the plenum and have burned very little oil since buying the home 4 years ago. I have found that whenever I have tried to use the furnace it takes a long time for it to heat up the water in the hx before it actually can send some decently hot air out of the vents. I average around 12 cords Of hardwood from November 1 to around May 1.
Now to the new System. I would like to try and cut down on my wood usage and would like an efficient back up system in the house that I can go away for the weekend and it will keep the owb warm and heat the house. I have purchased a heatmaster g200 to install this fall. It should help cut down on my wood usage. Second thing is that I have purchased a 10 year old Weil mclain gold series 185k btu oil boiler to replace the old oil furnace. I plan on removing the old oil furnace and installing the boiler in its place. I will tie the supply and return lines for the forced hot air together with a plenum that has the water to air hx and the blower in it. I plan to run the supply line from the owb through a flat plate hx on the boiler then to the water air hx then back to the boiler.
Now a couple questions. First is what size flat plate hx do you guys think I need?
Second question is about the proposed set up, any suggestions on it? Thanks!
Have you done a heat loss calculation for the house? it sounds like you need to have someone actually design a system for you. the oil boiler you have may be way too large. and are you heating hot air with the oil boiler?
karl
I have not had a heat loss calc done for the home. the old furnace was a 200k btu oil furnace. I have done some improvements such as attic insulation, wall insulation and air sealing. I have done my own manual j calc before and while I think I may be a little oversized I don't think I am way out of the ball park. Yes I plan on using the oil boiler to act as a hydro air system. The owb will pump 24/7 the loop of water. It will go from the owb to the oil boiler through the FP then to the 24x24 hx in the air handler then back to the owb. When the owb isn't running the oil boiler will heat the owb (195 gallons) which should act as a buffer tank to avoid short cycling of the oil furnace.
OK just checking. 185 Kbtu non modulating is a big boiler for most houses.
I'm a little fuzzy on the setup.
I think you said the OWB water would go OWB-FPHX-plenumHX-OWB?
Does that mean the FPHX heats up the oil boiler?
How would the oil boiler water go? Is there another separate plenum HX for it? Or how does the oil burner heat the plenum - is the only thing in the oil boiler circuit the FPHX?
You are correct. The only thing in the loop on the oil boiler would be the flat plate. The loop would simply be pumped(taco 007 would be fine I think) from the oil boiler, through the flat plate and then back into the oil boiler. This would keep the oil boiler at temperature except if the owb runs out of wood or I go away for a weekend. When the temp dropped down in the oil boiler the aquastat would kick it on and it would heat the water in the opposite direction. Instead of the OWB loop being heated by the OWB, the oil boiler would heat the loop which would for one keep the owb from freezing up and it would be able to heat the house because the loop goes through the water to air hx in the plenum and that would still work just as if the owb is still running. Did I clear it up at all? I am still wondering about sizing my Flat plate, I think the a 40 would do it, a 50 for sure but any suggestions on that are welcomed.
I don't have an OWB or even any second hand experience with them - and also don't have a hot air system or plenum HX. So take this for whatever it's worth - but I might consider rearranging the setup the other way, so the only thing on the OWB loop is the FPHX, and everything else is on the oil boiler. Otherwise, I think you would be sending quite a bit of oil-heated heat outdoors when the system is running in backup mode. The OWB would keep the indoor boiler up to temp, and the oil boiler pump would do all the circulating to the heating needs. Then if you are away long enough that a freeze up of something on the OWB side might be a concern, you could maybe use a timer setup for that that would run the OWB circ pump intermittently, say for 5 minutes every hour or something like that.
The thoughts of my oil boiler sending heat to a cold OWB that has its circ running 24/7 makes me shudder a bit - but hopefully others will add some more input. Don't think I can help a lot on the FPHX sizing. I have a 20 plate for my DHW side, that works great for it but pretty sure is not near big enough for what you want to do.
What exactly do you have for underground piping? Have you ever measured the heat loss in it?
I certainly don't dislike your approach with just running the water to the flat plate and back out to owb. I did think though that the owb would simply act like a buffer tank for the oil boiler keeping it from short cycling. I have homemade spray foam lines with about 3 degree loss in the 200ft loop.