NFPA 211 clearances

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.

jfog

New Member
Jan 21, 2021
6
bend oregon
No takers on my original question about mantel clearances so I will try again. I found the below attached NFPA 211 clearances on a stove mfg site. I do not know if the typos (% instead of ") comes from NFPA or the mfg. Anyhow, nowhere is there guidance on clearance to a wood MANTEL. A mantel is not a wall, and I do not think it is a ceiling either. Its wood so its combustible, but I still can't figure it out. It appears as though with proper shielding clearances to a ceiling can be reduced by 50%, but may not be less than 18" I would hope a wood mantel, which is not a ceiling, can be closer than 18". My stove spec is 24" to a mantel, so with shielding I would think 12" (50%). But that is less than 18". But its not a ceiling, so..... There are plenty of threads on this topic and posts with pictures which is helpful, but no answers as to code and NFPA 211. If you dropped a plumb line off the edge of my mantel it would probably overhang 1/3 the depth of my stove.

NFPA 211 clearances.PNG
 
My stove spec is 24" to a mantel
It is possible that the stove manufacturer did not test a reduced clearance for the mantel so it not listed or advised to reduce the actual clearance in the field.
 
It is possible that the stove manufacturer did not test a reduced clearance for the mantel so it not listed or advised to reduce the actual clearance in the field.
I imagine that is possible. There seems to be some disconnect in standards however as each manufacturer seems to have specs for alcove clearances, which vary, and then reference NFPA-211 for protected surfaces which are standardized. I guess I can find another stove manufacture with the same alcove clearance that did do mantel testing and just use their data.
 
Mantels in alcoves are not all that common. The first place to ask is the stove company's tech support. If they are ok with a mantel shield on spacers, ask for it in writing. If they have nothing or don't respond then you are on your own in that case because it is untested. It may be ok with a proper shield, but it depends on the mantel design and shielding. Note that the stovepipe also has clearance requirements too.
 
Mantels in alcoves are not all that common. The first place to ask is the stove company's tech support. If they are ok with a mantel shield on spacers, ask for it in writing. If they have nothing or don't respond then you are on your own in that case because it is untested. It may be ok with a proper shield, but it depends on the mantel design and shielding. Note that the stovepipe also has clearance requirements too.
My guess is that there is no way they would open themselves to that sort of liability. I did send them the question though. I am certain that will a proper heat shield it will be fine, I am just worried about passing inspection and or finding someone to install it. I do not think an installer will do it without code compliant clearances. There is probably a way around that, but then what? I guess you never have to get it inspected? I am in Oregon.
 
I did find this. So some company will sell you a product that cuts the clearance in half (just like 211). It’s cheap enough and probably gives you the best chance should anyone question the clearances.


The Mantel Protector attaches to your mantel and allows a clearance reduction from 36″ to 18″ from the top of an unlisted stove, as required by the NFPA 211 requirement.

I just looked at my manual and it says 24” too. No mention of reducing it.
 
My guess is that there is no way they would open themselves to that sort of liability. I did send them the question though. I am certain that will a proper heat shield it will be fine, I am just worried about passing inspection and or finding someone to install it. I do not think an installer will do it without code compliant clearances. There is probably a way around that, but then what? I guess you never have to get it inspected? I am in Oregon.
If the installation is to be inspected, then asking the inspector in advance if the heat shield would be acceptable is a good place to start. It should be ok but it's good to verify. An alternative would be to put in a non-combustible mantel.
 
  • Like
Reactions: Solarguy3500
My guess is that there is no way they would open themselves to that sort of liability. I did send them the question though. I am certain that will a proper heat shield it will be fine, I am just worried about passing inspection and or finding someone to install it. I do not think an installer will do it without code compliant clearances. There is probably a way around that, but then what? I guess you never have to get it inspected? I am in Oregon.
I would bet your inspector won't even notice. As far as the installer some won't do it without a spec some will sheild it and call that good and others will completely ignore the issue.
 
I did find this. So some company will sell you a product that cuts the clearance in half (just like 211). It’s cheap enough and probably gives you the best chance should anyone question the clearances.


The Mantel Protector attaches to your mantel and allows a clearance reduction from 36″ to 18″ from the top of an unlisted stove, as required by the NFPA 211 requirement.

I just looked at my manual and it says 24” too. No mention of reducing it.
I know I'm late to this discussion, but I have some questions about that heat shield. I was able to see the dimensions but unable to see many other specs on that website. Is it 24 gauge metal and does it come with all the hardware (spacers...etc)? Also, are you able to rip it to the width you need? Thanks for any info you can give me!
 
24 ga is fine. Sheet metal is typically cut with a shear, either with a large one in the shop or with a hand shear. It helps if you have some experience cutting metal. If not, take it to a local sheet metal shop and have them do it. However, don't cut it too small. It needs to extend past the stovetop.

The kit says it contains mounting hardware.
 
Last edited:
  • Like
Reactions: Ctwoodtick
24 ga is fine. Sheet metal is typically cut with a shear, either with a large one in the shop or with a hand shear. It helps if you have some experience cutting metal. If not, take it to a local sheet metal shop and have them do it. However, don't cut it too small. It needs to extend past the stovetop.

The kit says it contains mounting hardware.
Thanks for that info, begreen! Thankfully I have access to a metal brake so hopefully that will make it quick and easy...
 
Thanks for that info, begreen! Thankfully I have access to a metal brake so hopefully that will make it quick and easy...
A brake is for bending, this will require a shear for cutting.
 
  • Like
Reactions: Jmorg
I had great experience with a straight edge and metal cutting blade on my circular saw.
 
A brake is for bending, this will require a shear for cutting.
True, but if you lock it in and score it a few times then you can bent it all the way up and snap it off with the brake. Unless the metal is just too thick, but I don't think it will be...
 
True, but if you lock it in and score it a few times then you can bent it all the way up and snap it off with the brake. Unless the metal is just too thick, but I don't think it will be...
One would still need to cut through the metal at the 90º bend. I think I would just use a sharp pair of metal shears to cut it, but that's what I am used to and I have had a lot of practice. EbS-P had an alternative.
 
One would still need to cut through the metal at the 90º bend. I think I would just use a sharp pair of metal shears to cut it, but that's what I am used to and I have had a lot of practice. EbS-P had an alternative.

^This^
I have the Meecos mantle protector and I just took a look at it and it looks like 22 gauge or thicker steel. I don't know what you would score it with, but I don't think that approach will work.

As @begreen said, get a good pair of metal snips, specifically the Midwest brand. They make some really good offset right and left snips that are the only ones worth buying. Take that from someone who was a metal worker for 4.5 years.