I am wanting to install the Century CW2900 insert in my existing fireplace. It looks like as long as I add a non-combustible floor covering I will meet all clearances to combustibles except (I believe) the overhead clearance of 27" to combustible top surround and mantle shelf.
I have a 29" high opening with 3 rows of brick above, then mantle and then plaster wall above. This gives me ~40" total of non-combustible height before the plaster wall. The height of the Cw2900 is 22 5/8" and with the 27" of clearance I would think I need 49 5/8" of total height from the hearth floor. So I would be (49 5/8" - 40") = 9 5/8" short.
My plan would be to add either a 12"d slate noncombustible mantle or a 12" wood mantle with a 24g metal heat shield. Would this reduce the clearance needed to within my range?
The NFPA 211 states in section 13.6.2.3 that I can reduce clearances by 66% to a minimum of 12" for combustible walls, does that apply here? Or would it be that I can reduce by 50% to an 18" min for combustible ceilings (with the mantle being the ceiling)? Would either of these work for my situation to reduce the clearance required between the insert top and the plaster wall?
Thank you for your help!
I have a 29" high opening with 3 rows of brick above, then mantle and then plaster wall above. This gives me ~40" total of non-combustible height before the plaster wall. The height of the Cw2900 is 22 5/8" and with the 27" of clearance I would think I need 49 5/8" of total height from the hearth floor. So I would be (49 5/8" - 40") = 9 5/8" short.
My plan would be to add either a 12"d slate noncombustible mantle or a 12" wood mantle with a 24g metal heat shield. Would this reduce the clearance needed to within my range?
The NFPA 211 states in section 13.6.2.3 that I can reduce clearances by 66% to a minimum of 12" for combustible walls, does that apply here? Or would it be that I can reduce by 50% to an 18" min for combustible ceilings (with the mantle being the ceiling)? Would either of these work for my situation to reduce the clearance required between the insert top and the plaster wall?