odd behavior in gas furnace
RustyShackleford
1,753
NC
Trying to help stepson with a "gas pack" HVAC unit (a packaged unit that sits beside the house and incorporates an A/C and a natural-gas furnace). The gas furnace does not come on reliably.
The furnace has 3 burners, each an orifice in the side of a length of black pipe. The igniter lights the first one and then the flame jumps to the 2nd and then the third. The safety thermocouple/thermopile is on the 3rd burner, so it shuts the gas off unless all three light. This appears to be the normal behavior.
What often happens is that the first burner lights, but the flame fails to spread to the 2nd and 3rd burners and so the system soon shuts off; after 3 tries it gives up. If he cycles the thermostat (which I assume resets the low-voltage control circuitry in the unit), and does that several times, eventually it comes on properly.
We can't figure out what is causing this behavior. He did a half-assed attempt to clean the orifices but he said they didn't appear clogged. I guess the black pipe could be partially clogged, but if that's the cause why does it sometimes come on exactly the way it's supposed to (the three burners fire up in quick succession, and the 3rd has just as good a flame as the first) ? Could it be the valve is faulty and sometimes doesn't let enough gas pressure through ? Bad gas pressure to the house ?
Googling suggests low pressure and/or clogging. It just doesn't make sense to me that it fires up perfectly ... sometimes.
Tank or gas line?
If tank, does it depend on the outside temperature (influencing gas pressure)?
Gas line, should've said, natural gas.
Reactions: stoveliker
Need to check gas pressure, incoming and manifold, The crossovers are also likely dirty. It can be dangerous doing this by yourself. I suggest calling a pro this is likely an easy and cheaper fix.
Reactions: begreen
Yeah the flame sensor is at the opposite end from the igniter for this exact reason. Need to confirm all the burners lit successfully. Clean the burners. Since the first one always lights I would guess the crossovers are dirty.
I had this problem the crossovers were crusty from the intake air dumping on them. Rust from the humidity blocked them. Cleaned them up a couple times since I had the furnace.
Reactions: RustyShackleford
Don't know the make or age but there is a pretty high failure rate on the heat exchangers on this style unit especially if they are not maintenanced regularly.
To clean the crossovers use a wire brush and blow them out with high pressure air-nitrogen. After doing this and checking gas pressures you really need to do a combustion analysis. If you are able to get her running it is or should be normal for a maintenance to check the other items.
Keep us updated.
I had something similar with the gas stove, and the problem was that sometimes the gas valve would get stuck - it didn’t open completely, especially when the gas pressure in the line jumped a little. I cleaned the nozzles and checked the thermocouple; everything was normal, but the failures repeated. Sometimes the light «clapping» diagnostics on the gas line and valve helped - if everything worked after that, then the problem was in the valve. I would try to temporarily connect the pressure gauge and see if there are no pressure surges, and if possible, remove and examine the valve itself for a filling.
On my previous gas furnaces that would be dust crud buildup where the flame front is supposed to spread. I will never forget the time I paid the service guy $$$$ to blow it off.