Can anyone help here please?
We've had this OPOP pellet boiler for at least 6 years and it's always been running very well.
But the last few weeks it seems to be behaving differently and I don't know why.
Two storey detached house 192sq meters.
UFH and rads upstairs.
OPOP H430 30kw with Woody 5.99E Bio-comfort control panel.
Thermostat at top of buffer tank is set at 60 degrees.
Thermostat at bottom of buffer tank is set at 70 degrees.
The pellet boiler used to ignite automatically when the water in the buffer tank would drop to a certain temperature. The temperature on the boiler would go down to about 25 degrees. It would burn for a couple of hours (or for however long it took to heat the water in the buffer tank) at 100% Power. It would reach at least 79 degrees then it would stop and not come on again for hours or a day or until the next time the water in the buffer tank needed heating up again.
Now it seems the boiler is heating to about 72 or 73 degrees and the Power % starts to dropping down gradually. It's as if the boiler won't continue to burn on full Power 100% and bring the temperature up to nearly 80 degrees like it used to. The auger is dribbling in small amounts of pellets at intervals just as it used to before, but I can't understand why it won't bring the temp up to nearly 80 degrees and stop burning.
Other things I notice:
The pressure gauge on from of the boiler stays up at 3 bar.
The Boiler Temperature (User Setup) is set to 72 degrees.
The pump between the buffer tank and the pellet boiler also seems to be constantly running not sure if that was always the way.
Circumstances that have changed recently:
Not long ago I had to turn the speed of the pump for the rads in the house down from 3 to 1 to try reduce the hissing sound from the rads. Also we had power cuts from recent storms but never caused issues before.
I've been trying to understand the settings available on the control panel.
Very similar to this user manual http://www.kbf.ie/pdfs/nbe_scottemanual_v02.pdf.
I can access the User Setup and the Advanced/Tech Setup.
After cleaning out all the dust from the bottom of the silo and the auger and a delivery of new pellets there is no change. The boiler is still reaching up to 72 or 73 degrees, the auger continues to feed pellets into the boiler and the Power % is gradually going down. Has anyone seen this scenario before?
We've had this OPOP pellet boiler for at least 6 years and it's always been running very well.
But the last few weeks it seems to be behaving differently and I don't know why.
Two storey detached house 192sq meters.
UFH and rads upstairs.
OPOP H430 30kw with Woody 5.99E Bio-comfort control panel.
Thermostat at top of buffer tank is set at 60 degrees.
Thermostat at bottom of buffer tank is set at 70 degrees.
The pellet boiler used to ignite automatically when the water in the buffer tank would drop to a certain temperature. The temperature on the boiler would go down to about 25 degrees. It would burn for a couple of hours (or for however long it took to heat the water in the buffer tank) at 100% Power. It would reach at least 79 degrees then it would stop and not come on again for hours or a day or until the next time the water in the buffer tank needed heating up again.
Now it seems the boiler is heating to about 72 or 73 degrees and the Power % starts to dropping down gradually. It's as if the boiler won't continue to burn on full Power 100% and bring the temperature up to nearly 80 degrees like it used to. The auger is dribbling in small amounts of pellets at intervals just as it used to before, but I can't understand why it won't bring the temp up to nearly 80 degrees and stop burning.
Other things I notice:
The pressure gauge on from of the boiler stays up at 3 bar.
The Boiler Temperature (User Setup) is set to 72 degrees.
The pump between the buffer tank and the pellet boiler also seems to be constantly running not sure if that was always the way.
Circumstances that have changed recently:
Not long ago I had to turn the speed of the pump for the rads in the house down from 3 to 1 to try reduce the hissing sound from the rads. Also we had power cuts from recent storms but never caused issues before.
I've been trying to understand the settings available on the control panel.
Very similar to this user manual http://www.kbf.ie/pdfs/nbe_scottemanual_v02.pdf.
I can access the User Setup and the Advanced/Tech Setup.
After cleaning out all the dust from the bottom of the silo and the auger and a delivery of new pellets there is no change. The boiler is still reaching up to 72 or 73 degrees, the auger continues to feed pellets into the boiler and the Power % is gradually going down. Has anyone seen this scenario before?