Searched and haven't found a similar problem so here goes. 5yr old P68, been running fine burning 3tons/yr or so then started acting up this year. Starts and runs great in Room or Stove temp mode, problem is when we shut it down by turning the Fan selector to Off, it acts like it wants to shut down (Status light goes out, distribution blower shuts off) but every 60sec it bumps the auger for 1-2seconds, continuing to slowly feed a small amount of pellets into the burnpot and as a result, keeps burning and won't shut down. The only solution I've found to get it to shut down completely is to open the hopper for a few minutes to 'break the cycle' of the autofeed keeping the stove running. Couple times even doing this it came back to life and was back burning when I got up in the AM.
My understanding is the 'bump' every 60sec or so is part of the normal shutdown and is intended to prevent fire from backing up into the hopper......until the ESP drops to a low enough temp that the stove is confident the fire is too low to burn back into the hopper.
Cleaned stove thoroughly, cleaned ESP thoroughly and no change. Replaced the ESP this weekend and still does the same thing.
Thoughts? Thanks in advance for the help.
My understanding is the 'bump' every 60sec or so is part of the normal shutdown and is intended to prevent fire from backing up into the hopper......until the ESP drops to a low enough temp that the stove is confident the fire is too low to burn back into the hopper.
Cleaned stove thoroughly, cleaned ESP thoroughly and no change. Replaced the ESP this weekend and still does the same thing.
Thoughts? Thanks in advance for the help.