Howdy all, I was going to post this in the gear forum because this is in reference to a gas grill, but I thought all you gassers would be a better source of info. (so mods, please locate as appropriate if this is not the best spot)

Here it goes: I have a 500 gal. propane tank that is used for forced air home heating only. The pipe comes into/through my attached garage. There is a "T" and shutoff located within the garage (I had it plumbed in for future use of heater or whatever). The tank has a regulator on it. Pipe comes to outside wall of garage and this has another regulator that then gets feed into the home and to the furnace. If I wanted to pipe propane to my gas grill, should it be plumbed into the tank regulator side or the home regulator side?

Maybe a simple way to ask this is:
What pressure does a gas grill run at?
What pressure exits the propane tank (after reg.)
What pressure enters the home?

I have no problem with using the grill regulator in addition if need be.
 
Maybe a simple way to ask this is:
<>What pressure does a gas grill run at?<> <14" w.c. - generally about 11" w.c. (max)
<>What pressure exits the propane tank (after reg.)<> 10 psig (max)
<>What pressure enters the home?<> <14" w.c. again, generally about 11" w.c. (max)

<>I have no problem with using the grill regulator in addition if need be.<>

You'll probably need it...
 
So if I am reading this correctly: I should tap into the line that is at house pressure, then run it to the grill regulator? I hope so, that is by far the easiest connection for me.
 
Jags said:
So if I am reading this correctly: I should tap into the line that is at house pressure, then run it to the grill regulator? I hope so, that is by far the easiest connection for me.

Yep. Your pressure is already knocked down once. You won't even need the regulator at the grill...
 
DAKSY said:
Jags said:
So if I am reading this correctly: I should tap into the line that is at house pressure, then run it to the grill regulator? I hope so, that is by far the easiest connection for me.

Yep. Your pressure is already knocked down once. You won't even need the regulator at the grill...

I'm pick'in up what your lay'in down. Easy Peezy.
 